Rack Mount SmartUPS 1500 LCD - Not detected by Powerchute software

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Rack Mount SmartUPS 1500 LCD - Not detected by Powerchute software
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
115
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:16 AM . Last Modified: ‎2024-03-06 01:55 AM

0 Likes
2
602
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:16 AM . Last Modified: ‎2024-03-06 01:55 AM

Rack Mount SmartUPS 1500 LCD - Not detected by Powerchute software

Hello,

Hopefully someone may be be able to help me solve an issue with a new Rack Mount SmartUPS 1500 LCD. When the UPS was first installed and the Powerchute Business Edition was installed on the Windows 2008 Server the UPS was detected correctly. But, shortly after this communciation was lost. The steps I have done so far are:

1) Unplugged/plugged in serial cable. No connection showing in APC Software.
2) Troubleshooted COM1 port, changed bps to 2400 as recommended by PC. No connection showing in APC Software.
3) Ran driver update for UPS in device manager, drivers up to date.
4) Removed UPS from APC device config tool, added UPS to APC device config tool. No connection showing in APC Software.
5) Swapped Serial cable for a USB cable.
6) No connection showing in APC Software.
7) Removed UPS from APC device config tool, added UPS to APC device config tool. No connection showing in APC Software.
8) Stopped and restarted APC services.
9) No connection showing in APC Software.
10) Uninstalled all APC software. Reeboted Server
11) Ran APC Agent install - UPS not detected on COM1 Port

The server OS is a Windows Server 2008 R2 Standard.
The server has 1 COM Port
I am using the serial/ to RJ45 cable supplied with the UPS.
UPS is present within Device Manager.

Further advice would be gratefully received.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:16 AM . Last Modified: ‎2024-03-06 01:55 AM

0 Likes
0
601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:16 AM . Last Modified: ‎2024-03-06 01:55 AM

when you get some down time, can you try to braindead this UPS? to do that, you do need to power down the attached load and then turn off the UPS itself. disconnect any communication cables. remove the UPS from AC power/wall outlet and then go ahead and disconnect the battery for 8-10 seconds to reset the UPS. then reconnect the battery and hook everything back up.

also, i am not sure why whoever requested the baud rate be set to 2400 for this UPS since it sounds like an SMT1500 or SMX1500 of some type - can you confirm the exact UPS model number from the white sticker on the back of the UPS?

you mentioned trying USB. can you describe the cable between the server and UPS? does it have a part number? is this when you saw the entry in device manager?

lastly, what is the brand of the hardware on the server if you don't mind sharing?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:16 AM . Last Modified: ‎2024-03-06 01:55 AM

0 Likes
0
601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:16 AM . Last Modified: ‎2024-03-06 01:55 AM

I know I am late to reply but I want to say I pursued this through APC Telephone support and they sent me out a replacement UPS. I am fitting the UPS tomorrow.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:16 AM . Last Modified: ‎2024-03-06 01:55 AM

0 Likes
0
602
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:16 AM . Last Modified: ‎2024-03-06 01:55 AM

when you get some down time, can you try to braindead this UPS? to do that, you do need to power down the attached load and then turn off the UPS itself. disconnect any communication cables. remove the UPS from AC power/wall outlet and then go ahead and disconnect the battery for 8-10 seconds to reset the UPS. then reconnect the battery and hook everything back up.

also, i am not sure why whoever requested the baud rate be set to 2400 for this UPS since it sounds like an SMT1500 or SMX1500 of some type - can you confirm the exact UPS model number from the white sticker on the back of the UPS?

you mentioned trying USB. can you describe the cable between the server and UPS? does it have a part number? is this when you saw the entry in device manager?

lastly, what is the brand of the hardware on the server if you don't mind sharing?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of