Hi, I upgraded the AOS on my AP9606 installed in my MasterSwitch Plus to 3.2.6b. I then reinstalled the masterswitch APP v 2.0.0.
I can no longer access the device manager. Any ideas? What's the newest version of AOS I can use in the MasterSwitch? Also, is there a newer version of the MSP APP?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:31 AM . Last Modified: 2024-03-08 02:27 AM
hi,
what it looks like to me is that the masterswitch plus APP 2.0.0 only supports up to AOS 2.5.4.
i found all the files here: ftp://ftp.apc.com/apc/public/hardware/mswitch/firmware/msp/v200
i would try reflashing with the AOS 2.5.4 then the 2.0.0 msp APP again and see how that goes.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:31 AM . Last Modified: 2024-03-08 02:27 AM
hi,
what it looks like to me is that the masterswitch plus APP 2.0.0 only supports up to AOS 2.5.4.
i found all the files here: ftp://ftp.apc.com/apc/public/hardware/mswitch/firmware/msp/v200
i would try reflashing with the AOS 2.5.4 then the 2.0.0 msp APP again and see how that goes.