AP9537 NMC Console no Xmodem can't FTP - Bricked and SOLVED

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9537 NMC Console no Xmodem can't FTP - Bricked and SOLVED
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
mikeinnyc
Ensign mikeinnyc
Ensign

Posted: ‎2022-09-05 10:37 AM . Last Modified: ‎2022-09-05 07:56 PM

0 Likes
2
3227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-05 10:37 AM . Last Modified: ‎2022-09-05 07:56 PM

AP9537 NMC Console no Xmodem can't FTP - Bricked and SOLVED

Hello,

I hope that someone here can help save this device.

With multiple Smart APCs and Netbotz I got confused and flashed the wrong IP Netbotz firmware. I immediate stopped the update from happening midway and bricked the device.

 

Using the proper cable, I am finally able to login to the console. The one with the headset pin APC 940-0299A 2.5mm to serial DB9 Female Console Cable is the proper cable.

 

Now I am able to see the directory tree but I can't use Xmodem. I used teraterm "Kermit" to transfer the bin files in order but to no avail. All its doing is printing garbled info on the terminal. When the upload is complete there is no .bin file in the root directory.

I tried FTP client after setting up an Static IP address -i 192.168.1.100, -s 255.255.255.0, - g 192.168.1.1. When I type tcpip I do see the proper address and as a result I can ping it from a LAN computer as well as from the console.

 

What I can't do is get these files either FTP or directly attached with the console. FTP won't let me even connect with APC APC and it seem the same with teraterm. Does APC user even allow this? Just keeps doing nothing.

 

I'm using an old school computer with a fresh windows 10 no updates.

 

I'm at a loss and need help.

 

Thanks

Mike

Attachments
  • Tags:
  • APC 940-0299A
  • borked firmware
  • english
  • NMCFirmwareUpdateUtility
  • SRT5KRMXLT
  • Tera Term
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mikeinnyc
Ensign mikeinnyc
Ensign

Posted: ‎2022-09-05 07:44 PM . Last Modified: ‎2022-09-05 08:04 PM

In response to mikeinnyc
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-05 07:44 PM . Last Modified: ‎2022-09-05 08:04 PM

 

Ok, I got fed up with the old school windows computer and went to an updated rarely used Windows 11 computer. Pinged my APC so we could talk to the unit then tried FTP. This time the FTP worked!!! Holy cow windows 11 worked even though Ubuntu dual boot is my flavor. Just make sure you cd into the directory where the .bin file is. run cmd as admin then cd to your file. This was so fast I couldn't believe it. It took me hours using teraterm kermit but got me at least here. She was dead nothing and I brought her back to life. I hope this helps someone who got kicked in the Nuts a few times as this was a challenge to fix. here's the link I followed https://www.apc.com/us/en/faqs/FA156047/#FTP 

apc console update7.jpg

 

solved.jpg

See Answer In Context

  • Tags:
  • bring back to life
  • console
  • english
  • reflashed
  • unbricked
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
mikeinnyc
Ensign mikeinnyc
Ensign

Posted: ‎2022-09-05 04:08 PM . Last Modified: ‎2022-09-05 04:16 PM

0 Likes
1
3202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-05 04:08 PM . Last Modified: ‎2022-09-05 04:16 PM

ok so super user is not "sudo."

Figured that out when I created a user "mike" with administrator permissions. (see attached pic)

then I just checked "users" to see my proper permissions.

That problem is solved but now I have another. I checked my good working APC for differences and boy did I find a problem.

here's where everything is wrong:

Apc Boot Monitor = v1.0.9 which is correct

Apc AOS = v 7.0.8 which is correct

Application Module list Apc AOS bin firmware v 7.0.8 which is incorrect.

 

Why do I have the application module listed as AOS? I already have that and now I have that twice!

 

Order of operations is wrong now what? I'm definitely not going to delete the apc_hw05_aos_708.bin.

I'm just trying to push via kermit apc_hw05_sumx_708.bin file for the application module.

 

I'm stuck deeper. I better stop and wait for help.

 

Attachments
  • Tags:
  • english
  • kermit
  • Tera Term
Reply

Link copied. Please paste this link to share this article on your social media post.

mikeinnyc
Ensign mikeinnyc
Ensign

Posted: ‎2022-09-05 07:44 PM . Last Modified: ‎2022-09-05 08:04 PM

In response to mikeinnyc
0 Likes
0
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-05 07:44 PM . Last Modified: ‎2022-09-05 08:04 PM

 

Ok, I got fed up with the old school windows computer and went to an updated rarely used Windows 11 computer. Pinged my APC so we could talk to the unit then tried FTP. This time the FTP worked!!! Holy cow windows 11 worked even though Ubuntu dual boot is my flavor. Just make sure you cd into the directory where the .bin file is. run cmd as admin then cd to your file. This was so fast I couldn't believe it. It took me hours using teraterm kermit but got me at least here. She was dead nothing and I brought her back to life. I hope this helps someone who got kicked in the Nuts a few times as this was a challenge to fix. here's the link I followed https://www.apc.com/us/en/faqs/FA156047/#FTP 

apc console update7.jpg

 

solved.jpg

  • Tags:
  • bring back to life
  • console
  • english
  • reflashed
  • unbricked
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore