Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-29 04:29 PM
I have two SmartUPS 5000's that seem to be working fine, BUT, in their logs, they only ever show self test Starting, never Passing.
(Screenshot attached)
Date | Time | Event |
Date | Time | Event |
2022-06-29 | 18:23:15 | System: Configuration change. Event log web display time selection. |
2022-06-29 | 18:23:07 | System: Configuration change. Event log web display time selection. |
2022-06-29 | 18:12:08 | UPS: Started a self-test. |
2022-06-29 | 02:13:39 | UPS: Started a self-test. |
2022-06-29 | 02:12:09 | System: Configuration change. BOOTP server address. |
2022-06-29 | 02:12:09 | System: Configuration change. BOOTP server address. |
2022-06-29 | 02:10:36 | System: Configuration change. BOOTP server address. |
2022-06-29 | 02:10:36 | System: Configuration change. BOOTP server address. |
2022-06-24 | 19:39:31 | UPS: Started a self-test. |
2022-06-17 | 19:39:25 | UPS: Started a self-test. |
2022-06-10 | 19:39:16 | UPS: Started a self-test. |
2022-06-06 | 18:17:57 | UPS: Started a self-test. |
2022-06-05 | 08:00:37 | UPS: Started a self-test. |
These SmartUPS 5000's have AP9617 management cards running sumx v3.9.3 on aos v3.9.4.
I have another device, a Symmetra 80K with an AP9630 running sy3p v7.0.4 on aos v7.0.4 and it logs the start and end of each self-test.
Is that an intentional difference between the 3.xx and 7.xx series FWs? or in the capability of the 9617 vs 9630 cards to detect the test completion?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-05 08:01 PM
Hi @ojfsdi
Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. Apologies for the late revert on this post.
I was able to find n article that will be able to assist you. Basically, you would need to find the code for the self-test passed and manually configure it.
Please the article below for your reference:
Video: Configuring clearing events with APC Network Management Cards
Link copied. Please paste this link to share this article on your social media post.