AP7920 firmware upgrade failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7920 firmware upgrade failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:12 AM

0 Likes
6
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:12 AM

AP7920 firmware upgrade failure

I've got a few AP7920s that I was upgrading to the latest firmware prior to setting up SNMP management for them. Unfortunately, the oldest ones, which were running 1.16 didn't upgrade sucessfully. Aos 2.02 seems to have loaded but the devices still report as 1.16. Loading 2.02 manually via FTP works but does the same. So I have no compatible application software, and can't upgrade to the latest Aos.

Any ideas?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:11 AM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:11 AM

Just this one doesn't like it or did you not try any others? Seemed like you had more than one with this issue?


I have two on the 1.1.6 firmware; I haven't tried the rPDU 1.0.2 application on both yet.


I am thinking can you try now AOS 2.0.2, let it reboot, try AOS 3.7.4, reboot then rpdu 3.7.4?

Unfortunately, that appears to take me back where I started; AOS 2.0.2 loads but does not boot.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:12 AM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:12 AM

Hello.

Can you clarify, where are you seeing the devices still report was 1.1.6? The normal process for this would be to load AOS 2.0.2, then AOS 3.7.4 (assming 2.0.2 becomes loaded into RAM), then rpdu APP 3.7.4. This is an exception where you load two AOS's in a row and it is OK to do so.

Depending on what you say to the above, I am interested to understand that when you log in via FTP, what does the FTP log in prompt say for the active AOS? And once you log in via FTP and do an ls (letter L) command, what files are shown there?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:11 AM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:11 AM

Can you clarify, where are you seeing the devices still report was 1.1.6?

In the login banner for Telnet and FTP

American Power ConversionNetwork Management Card AOS 

v1.1.6

220 AP7920 Network Management Card AOS v1.1.6 FTP server ready.

And once you log in via FTP and do an ls (letter L) command, what files are shown there?

apc_hw02_aos_116.bin

About system shows 202 and 116 in flash though:

    Description : Network Management Card AOS
    -----------------------------------------------------------------------
    Name    : aos           Type    : APC OS
    Version : 202           Sector  : 39
    Date    : 12/29/2003    Time    : 13:54:07
    CRC16   : EDB9

    Press to continue...

    Description : Network Management Card AOS
    -----------------------------------------------------------------------
    Name    : aos           Type    : APC OS
    Version : 116           Sector  : 63
    Date    : 02/07/2003    Time    : 13:45:39
    CRC16   : 9A88


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:11 AM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:11 AM

When you loaded it manually, did you verify you did the FTP file transfer in binary mode? Please check for that.

What we will need to do is load the rpdu application that bundles with AOS 1.1.6 back into the NMC. So FTP that back on (attached to this post) and make sure that afterwards, you log in and it shows rpdu v1.0.2, and AOS 1.1.6 and everything is fine as when you started.

Then, we'll try AOS 2.0.2, see if that loads properly after disconnecting and letting the NMC reboot, then AOS 3.7.4, allow time for a reboot, then rpdu 3.7.4.

Let me know if you have any questions before you start.

Attachments
apc_hw02_rPDU_102.bin.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:11 AM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:11 AM

It loads the rpdu software but it's not entirely happy with it:

American Power Conversion               Network Management Card AOS      v1.1.6
(c) Copyright 2002 All Rights Reserved  Rack PDU APP                     v1.0.2
-------------------------------------------------------------------------------
Name      : Unknown                                   Date : 04/10/2014
Contact   : Unknown                                   Time : 15:36:54
Location  : Unknown                                   User : Administrator
Up Time   : 0 Days 0 Hours 12 Minutes                 Stat : P+ N+ A-

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:11 AM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-18 12:11 AM

Just this one doesn't like it or did you not try any others? Seemed like you had more than one with this issue?

I am thinking can you try now AOS 2.0.2, let it reboot, try AOS 3.7.4, reboot then rpdu 3.7.4? Since both files are in there, I am thinking that might work..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:11 AM

0 Likes
0
1642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-18 12:11 AM

Just this one doesn't like it or did you not try any others? Seemed like you had more than one with this issue?


I have two on the 1.1.6 firmware; I haven't tried the rPDU 1.0.2 application on both yet.


I am thinking can you try now AOS 2.0.2, let it reboot, try AOS 3.7.4, reboot then rpdu 3.7.4?

Unfortunately, that appears to take me back where I started; AOS 2.0.2 loads but does not boot.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore