AP7723 automatic transfer switch - is it suitable?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7723 automatic transfer switch - is it suitable?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

0 Likes
3
1055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

AP7723 automatic transfer switch - is it suitable?

I'm thinking of purchasing a SURT6000XLI to protect an intel blade server: http://www.intel.com/content/www/us/en/modular-server/modular-server.html

I would like to have dual power redundancy but unfortunately the intel blade needs 3 out of 4 PSUs to run(they are 1000watt each). I was thinking of getting a AP7723 auto transfer switch, plug source A into the SURT6000XLI, Source B into mains.

The 4 PSUs of the blade server in turn would be plugged into the AP7723

Would the AP7723 be designed for such purpose? With 4 sockets left i also hope to plug in couple mmore servers,router and firewall as well. Would auto transfer switch be able to handle the load?

Thanks

Wil

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

0 Likes
0
1055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

i think as long as it does not have any of the issues mentioned above that a generator has then it should be fine.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

0 Likes
0
1055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

We (APC/Schneider Electric) recommend placing a UPS between the generator and the ATS input. The UPS will condition the input voltage to the ATS to prevent thrashing. A second UPS should be used between the power utility and the other input of the ATS (which you already mentioned would be the SURT6000). This UPS will power the load while the generator starts and stabilizes. The UPS should be sized to allow time for the generator to be started and the time needed for the UPS attached to the generator to operate normally.

While the generator is starting, the generator voltage and frequency are not stable. If the ATS is connected directly to the generator, the ATS can switch to the generator input before the generator has stabilized. The load of the ATS will cause the generator voltage to dip.This dip can also shift the frequency of the voltage. Either of these issues can cause the ATS to switch to the other input.

even so, if you need to do this, then you will want to make sure you configure the ATS to have a low sensitivity and wide transfer range in order to best handle the generator directly.

When the ATS switches inputs, the ATS waits for a zero crossing of the voltage waveform. If the load has a power factor of less than 0.9, there can be significant current flowing. This will lead to arcing and welding of contacts.

Relay manufacturer specify contact life for resistive loads only and switching on the zero crossing. They won’t specify contact life at different power factors. Engineering cannot predict how long the contacts will last if switching loads with low power factors. Engineering does not recommend using the ATS with loads that have a power factor of 0.9 or less.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

0 Likes
0
1055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

Many thanks.

I will not be using the diesel generator for second source though (it will be just mains) The ATS will be using Source A (SURT6000) at all times unless theres maintenance planned or the UPS fails

Is this still ok?

Wil

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-13 01:56 AM

i think as long as it does not have any of the issues mentioned above that a generator has then it should be fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of