A phase synchronization fault exists.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • A phase synchronization fault exists.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:22 AM

0 Likes
4
3454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:22 AM

A phase synchronization fault exists.

I have a site with an MGE Galaxy 3500 10 kVA, there is also a backup generator for the location.
When they loose power and the generator starts I get the following messages on the UPS:
10/21/2012 18:47:23 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
10/21/2012 18:47:08 UPS: No longer on battery power.
10/21/2012 18:47:03 UPS: An input voltage or frequency problem prevents switching to bypass mode.
10/21/2012 18:47:03 UPS: On battery power in response to an input power problem.
10/21/2012 18:42:56 UPS: A phase synchronization fault no longer exists.
10/21/2012 18:42:56 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
10/21/2012 18:42:35 UPS: A phase synchronization fault exists.
10/21/2012 18:42:35 UPS: No longer on battery power.
10/21/2012 18:42:27 UPS: On battery power in response to an input power problem.
10/21/2012 18:42:25 UPS: An input voltage or frequency problem prevents switching to bypass mode.
Is there an issue with the power being supplied from the generator?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:22 AM

0 Likes
0
3449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:22 AM

Sorry it didn't added the subject:
10/21/2012 18:47:23 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
10/21/2012 18:47:08 UPS: No longer on battery power.
10/21/2012 18:47:03 UPS: An input voltage or frequency problem prevents switching to bypass mode.
10/21/2012 18:47:03 UPS: On battery power in response to an input power problem.
10/21/2012 18:42:56 UPS: A phase synchronization fault no longer exists.
10/21/2012 18:42:56 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
10/21/2012 18:42:35 UPS: A phase synchronization fault exists.
10/21/2012 18:42:35 UPS: No longer on battery power.
10/21/2012 18:42:27 UPS: On battery power in response to an input power problem.
10/21/2012 18:42:25 UPS: An input voltage or frequency problem prevents switching to bypass mode.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:22 AM

0 Likes
0
3450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:22 AM

Sorry it didn't added the subject:
10/21/2012 18:47:23 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
10/21/2012 18:47:08 UPS: No longer on battery power.
10/21/2012 18:47:03 UPS: An input voltage or frequency problem prevents switching to bypass mode.
10/21/2012 18:47:03 UPS: On battery power in response to an input power problem.
10/21/2012 18:42:56 UPS: A phase synchronization fault no longer exists.
10/21/2012 18:42:56 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
10/21/2012 18:42:35 UPS: A phase synchronization fault exists.
10/21/2012 18:42:35 UPS: No longer on battery power.
10/21/2012 18:42:27 UPS: On battery power in response to an input power problem.
10/21/2012 18:42:25 UPS: An input voltage or frequency problem prevents switching to bypass mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:21 AM

0 Likes
0
3449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:21 AM

yes, thats what it sounds like, especially since the fault happens with the generator. do you have the data log for that time period too? sounds like the three phases are out of sync.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:21 AM

0 Likes
0
3450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:21 AM

Yes I have attached the data log.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:21 AM

0 Likes
0
3449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:49 AM . Last Modified: ‎2024-03-13 01:21 AM

i had someone more experienced with this UPS take a look at the issue.

One thing we would like to know is if the items reported by the NMC between 18:42 and 18:47 are when the generator was running. These events could be a result of a utility failure but they could also be the same events if the UPS does not like the generator output.The G3500 has a maximum slew rate of 1Hz/s. Slew rate is how fast the output voltage is allowed to change. So if the UPS is having difficulty tracking the input waveform, (if it is changing faster than 1 Hz/s) then the UPS will not be able to synch to mains. If this is a single mains UPS (they almost always are) then the bypass and the mains are the same input. Therefore, the UPS can't sync to bypass either.

So the UPS goes to battery until the input waveform clears up. This is typical behavior for small, highly loaded or old generators, or huge generators that have very little load on them.

if you have any further issues or this does not seem correct, it was suggested that you contact our 3 phase power team for further assistance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of