A little story and a few questions.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • A little story and a few questions.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
4
943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

A little story and a few questions.

My rack mount UPS (SU700RM2U) failed one day, along with some beeping and odd flashing of lights. So I unplugged everything, switched over to a backup UPS, and let the unit sit charging for a day, hoping it would recharge the batteries. I came back and was greeted by the same beeping and failure to power anything. Pulled out the DVM and the batteries were reading 13.10V, not quite the 24V to be expected. I realized I would now have to take out the batteries, a task that proved harder than ever imagined. As I was pulling out the tray it nearly immediately got stuck, and I noticed the batteries were swollen. Clearly they had been overcharged.

I was able to force the first battery out, but the second, not a chance. I've seen this happen to a few SLAs, but never anything as bad as the second battery. I now had to remove the rack, take of the top, bend a bunch of steel, and finally it came out. Finally I thought I was done, but no. The combination of the pressure on the sidewall and retaining plate from the expansion and the tape on the batteries forced me to pry the batteries out with a chisel and a hammer.

Some photos:
http://i.imgur.com/4sS1H.jpg
http://i.imgur.com/H0m6Q.jpg

Now the questions. I obviously understand I need new batteries, but how can I test the charging circuit to ensure it won't just overcharge them again? Was it a fluke, or a full failure?
Second, I notice the unit has space for 4x 12VSLAs, any downside to wiring two more in?

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

What was the ambient temperature?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

How long had those batteries been in service in the UPS? Under ideal conditions (reasonable temperature, not discharged often or deeply), service life can run from 3 to 5 years or so.

Regardless of manufacturer, the smaller (< 5KVA or so) UPS market is extremely price-sensitive, and charging and monitoring circuits are not as elegant as they might possibly be.

Even in a battery system with very sophisticated monitoring (thermal sensors on one terminal on every battery in the string, current and voltage monitoring) and in a non-cost-sensive market (I'm specifically talking about telco remote battery plants), there are failure modes that will not be detected until a tech arrives for an unrelated reason and discovers the smell of burnt batteries.

I assume your UPS is out of warranty? You should consider the cost of replacement batteries vs. moving to a new UPS (possibly larger capacity if warranted, more features, etc.). I've gotten good deals from APC in the past (mostly on larger units - Matrix and Symmetra). There are (or at least there were, I'm not really up-to-date on this), 3 different APC programs. First was simply buying a replacement battery pack (RBC). Next was the Charge-UPS® program which provided the battery pack and an additional 2 years of warranty (subject to eligibility). Top was Trade-UPS® which provided a whole new UPS with factory warranty.

If you decide to just replace the batteries, I'd suggest checking the manufacturing date of the batteries (normally thermally embedded into the battery case, as shown in your photo). That's not the assembly date (which will be on the APC barcode sticker if genuine APC, or in random other places if aftermarket). Some resellers have these batteries sitting around in inventory, discharging. In one particularly bad case, "new" batteries I purchased (for a non-APC application) actually had a date code from two years prior.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

Even if there are space for four(4) batteries, the UPS/charging circuit is designed for only up to 2 batteries on it. Also, we are no longer offering the Charge-UPS. Considering on what happened to your unit, I would suggest getting a new UPS via the TradeUPS program.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

The float voltage of these units is set too high, thus killing the batteries..
I guess APC was hoping to get some extra revenue (they sell the battery packs, too), but people went to other vendors after that.

And with most of those old units it cannot be set easily, unless you solder some resistors.

But I wouldn't go throught the hassle for such an old unit.

See my other thread, and search for "APC float voltage".

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

What was the ambient temperature?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore