can SURT5000XLT be connected to split phase 240V

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • can SURT5000XLT be connected to split phase 240V
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
5
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:02 AM . Last Modified: ‎2024-03-13 03:20 AM

can SURT5000XLT be connected to split phase 240V

Hi all,
I read in the manual that the SURT5000XLT can be programmed to accept 240V instead of (the 2 phase) 208V.

But it doesn't say in the manual if it can it be used with a split phase 240V?

The building has only 2x120 (i.e. split phase).

Can it be done? Has anybody tried?

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 240v
  • phase
  • split
  • surt5000xlt
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

no problem 🙂

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

yes, you can do that. the UPS just cares that it has 240v input (assuming you meant you have 2 hots and a ground connection available). then, you need to configure the UPS and tell it you are inputting 240. the only note is that then it will not output 240 split phase so don't expect that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

Hi,
the building has 2x120V (split phase) as mentioned.
By using the two "hot" ends (let's call them V1 and V2) you get 1x240V.

Split-phase is used in the US for homes and very small businesses.
see
http://en.wikipedia.org/wiki/Split-phase_electric_power

This building was a hotel and was transformed into individual businesses.

From what I understand these UPS rectify whatever they get into DC, and convert that DC into AC.
Their input can be anywhere form 160V upto 270V (AC).

So my question is if it would work if I simply connect the one phase input of the UPS to V1 (the one end of the split phase), and it's other input to V2 (the other end of the split phase).

So the UPS still "sees" the full potential of 240V on its inputs.

If if we take it technically:
I don't know if the internal capacitors -which store the DC energy- are capable to fill in for the missing timeshifted second phase or not.

I would not draw the full power from this UPS, maybe around 1.5KW at maximum.

Would that work?

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

the 240v input should be two phases of 120v that are 180º out of phase. i think that what you are describing will fine as long as you input a ground connection with it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

Thanks for that!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:03 AM . Last Modified: ‎2024-03-13 03:20 AM

no problem 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of