Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
I have a 3000XLT with 3 external UXABP48 battery packs purchased in may 2011. I am getting 0 to 20 minute runtime with a 42% load. Any test I do it goes to battery discharge or low condition. What do I need to do?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
Are you using any software or a network management card? I would first make sure either one is configured to show the number of external batteries so it will give you the proper runtime.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
Are you using any software or a network management card? I would first make sure either one is configured to show the number of external batteries so it will give you the proper runtime.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.