APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
I have a 3000XLT with 3 external UXABP48 battery packs purchased in may 2011. I am getting 0 to 20 minute runtime with a 42% load. Any test I do it goes to battery discharge or low condition. What do I need to do?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
Are you using any software or a network management card? I would first make sure either one is configured to show the number of external batteries so it will give you the proper runtime.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
Are you using any software or a network management card? I would first make sure either one is configured to show the number of external batteries so it will give you the proper runtime.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.