I have a 3000XLT with 3 external UXABP48 battery packs purchased in may 2011. I am getting 0 to 20 minute runtime with a 42% load. Any test I do it goes to battery discharge or low condition. What do I need to do?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
Are you using any software or a network management card? I would first make sure either one is configured to show the number of external batteries so it will give you the proper runtime.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:59 AM . Last Modified: 2024-03-13 01:58 AM
Are you using any software or a network management card? I would first make sure either one is configured to show the number of external batteries so it will give you the proper runtime.