A backfeed relay fault exists.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • A backfeed relay fault exists.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

0 Likes
7
12809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

A backfeed relay fault exists.

Hello,

I have a Smart-UPS RT 5000 XL
SN: NS0935003966
Firmware Revision: 3
Manufacture Date: 08/24/2009
Apparent Power Rating: 5000 VA
Real Power Rating: 3500 W

UPS installed 1 month ago, and I have no problem with it. The main power source is generator that start 6 AM and turned off 8 PM everyday. So the battaries discharge everyday and charge again in the morning.
The problem i found today when i came to the office, is the front panel of UPS [X] is in red color and there was no outpout power and all equipments is off; I turned off the UPS and run it again and everything back to normal;

That happened 3 days ago, and I had to do the same thing, And no one stays to 8PM to monitor whats happening when the generator turned off and battary discharged.
Log attached.

Appreciate your help!

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • smart-ups
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

0 Likes
0
12805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

Hi Buzz,

Appreciate your response!
And hope you can help me out solving this issue.

It happend again this morning, and I think it gonna happen on a daily basis. Please advise from where I can get the data log?

Your diagnoses that a problem happened and the UPS tried to go to ByPass mode and it fail.
I don't understand the log 100%; When a generator turned off the UPS supposed to run on battary untill the battary approch to ran out and then send notifications and shut down itself?

If you please can you explain the sequance of [Input Power not exist, run on battary, UPS closed]; What is the ByPass mode and when It supposed to move to ByPass?

In the back panel the ByPass switch is adjusted to Online, is that right?

Regarding the battary discharge everyday; Ya the genrator turned off everyday at 8 PM, so the equipments consume the power for 2 hours before the UPS battary ran out. and then UPS suppose to turn itself off, when the generator run again in the morning, the UPS should start automatically.
It did like this the last 30 days, but the last few days started to show these errors and that affect the business.

I have no other options as we In Afghanistan, and there Is no power source but generators

Attached some pictures, for the log screen is that the data log.
Really appreciate your support.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

0 Likes
0
12805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

So this has happened twice since you installed it a month ago? Could you also post the data logs?

From just the data logs you provided, it at least looks like the UPS tried to go to bypass when it detected the problem, but it couldn't because there was no input power... So of course, it turned off.

Just to understand exactly how this is being used, are you saying the unit is on battery from 8pm till 6am every day? If that's the case, you're going to kill those batteries pretty quickly...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

0 Likes
0
12806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

Hi Buzz,

Appreciate your response!
And hope you can help me out solving this issue.

It happend again this morning, and I think it gonna happen on a daily basis. Please advise from where I can get the data log?

Your diagnoses that a problem happened and the UPS tried to go to ByPass mode and it fail.
I don't understand the log 100%; When a generator turned off the UPS supposed to run on battary untill the battary approch to ran out and then send notifications and shut down itself?

If you please can you explain the sequance of [Input Power not exist, run on battary, UPS closed]; What is the ByPass mode and when It supposed to move to ByPass?

In the back panel the ByPass switch is adjusted to Online, is that right?

Regarding the battary discharge everyday; Ya the genrator turned off everyday at 8 PM, so the equipments consume the power for 2 hours before the UPS battary ran out. and then UPS suppose to turn itself off, when the generator run again in the morning, the UPS should start automatically.
It did like this the last 30 days, but the last few days started to show these errors and that affect the business.

I have no other options as we In Afghanistan, and there Is no power source but generators

Attached some pictures, for the log screen is that the data log.
Really appreciate your support.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

0 Likes
0
12805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

Hi,

I found the data log,

Showing the last 2 days.

Thanks!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

0 Likes
0
12805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

I figure there's something wrong with the UPS. The backfeed relay fault error message is clearly not one of normal operation, so you may want to call tech support for your region to try some troubleshooting steps and get a replacement, if necessary.

When you see the fault LED on the front (I think you said you saw that once before?) were there any other lights on the front display? The battery bar graph should light up in a pattern to indicate what the fault is. Sometimes the fault reported on the display is different from the one reported in the NMC. If you can't remember, I would probably try to force the unit on battery so you can actually see what happens, though I would have your equipment plugged into something else for this test in case it drops again, of course. Tech support would probably suggest this, too.

I apologize for confusing you about bypass. The "online" position of the switch is normal operation, yes. However, when the UPS detects a fault that would cause it to turn off, it tries to automatically go to bypass first to keep your equipment powered. However, in this instance the fault is always appearing when there's no input power, so it can't go to bypass... it can't run on battery because of its fault and it can't go to bypass because your generator is off. Either way, your equipment will turn off.

The "bypass not in range" messages just mean that the input voltage or frequency isn't within normal operating range - in your case, the generator is turned off. Those are just warning messages to tell you it can't go to bypass if there's a fault. Normally, yes, the UPS is supposed to run on battery and then shutdown gracefully, just like it had been for the past 30 days before this issue occurred.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

0 Likes
0
12805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

Thanks Buzz,

- I'll try to contact support they may help.

- When I faced that error all LEDs was OFF except the Fault LED in Red colore was ON; UPS turnbed OFF and back ON; started normally! Battary Bar was off I think.

- Yesterday I spent sometime to see the UPS untill it shutdown. it spent lots of time while the remaining time is 0 minutes; but after sometime I found the [Online & Overload] emitted -> [On Battary & Fault] emitted -> [ByPass & replace battary] emitted. with a sequance. Maybe that light indication means out of battary power; When I turned the input voltage again On; the UPS started normally without any issues.

- Regarding the ByPass I imagine 3 cases A-"Internal Fault during the presence of input voltage the UPS tries to move to ByPass to power connected devices" B-"The switch moved manually to ByPass for a reason" C-"No input voltage existed and the UPS run on battary power UPS tries to go to ByPass which is make no sense"

- For case C; showing error "Input Voltage or Frequancy cannot support ByPass" is not logic;

- Something I notice; After the generator turned off; equpments keep consume the battary power untill battary ran out; at that moment when battary consumed and before UPS turned off; the fault happen "A backfeed relay fault exists" and UPS can't switch to ByPass as there is no Input voltage to switch to; In the morning when the input voltage come back; UPS starts BUT with the fault reported at night.

Untill I get help from support hope anyone can help me!

Appreciated!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

0 Likes
0
12805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

We have got a like incident, but with 2 UPSes in the same time.
There're 2 SURTD5000XLI, with 1 ext.bat.module SURT192XLBP both.
They work on the stable input power at the normal conditions.
3.09.2010 after a few black-outs (with durations from seconds to 1-2 minutes, properly changing to the battery power) at the almost same time they exposed 'A backfeed relay fault exists' and drop output power. See event.log (data.log records of 3.09 have been deleted as older than flash memory can host), I've downloaded them yesterday.
1st UPS - in chronologically accending order
03.09.2010 06:20:27 UPS: On battery power in response to distorted input. 0x0109
03.09.2010 06:32:43 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
03.09.2010 06:32:43 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
03.09.2010 08:58:18 UPS: Bypass not in range; low voltage. 0x020F
03.09.2010 08:58:18 UPS: On battery power in response to low input frequency. 0x0109
03.09.2010 08:59:33 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
03.09.2010 08:59:34 UPS: No longer on battery power. 0x010A
03.09.2010 09:00:03 UPS: Bypass not in range; low frequency. 0x020F
03.09.2010 09:00:03 UPS: On battery power in response to low input frequency. 0x0109

03.09.2010 09:00:04 UPS: A backfeed relay fault exists. 0x016B

03.09.2010 09:00:04 UPS: No longer on battery power. 0x010A

03.09.2010 09:00:04 UPS: The output power is turned off. 0x0114

03.09.2010 09:01:20 UPS: Bypass not in range; low frequency. 0x020F
03.09.2010 09:05:28 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210

03.09.2010 09:42:47 UPS: A backfeed relay fault no longer exists. 0x016C

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

0 Likes
0
12805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:59 PM . Last Modified: ‎2024-03-14 01:08 AM

03.09.2010 09:42:58 UPS: The output power is now turned on. 0x0113

03.09.2010 09:43:06 UPS: Started a self-test. 0x0137
03.09.2010 09:43:15 UPS: passed via internal operation a self-test. 0x0105

At the 09:40 -42 my colleague push the TEST button (start the both UPSes manually), and the next messages show the normal start...

2nd UPS
03.09.2010 03:41:07 UPS: No longer on battery power. 0x010A
03.09.2010 03:47:28 UPS: Bypass not in range; low voltage. 0x020F
03.09.2010 06:07:34 UPS: On battery power in response to rapid change of input. 0x0109

03.09.2010 03:47:31 UPS: No longer on battery power. 0x010A
03.09.2010 03:47:29 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
03.09.2010 03:47:28 UPS: On battery power in response to rapid change of input. 0x0109

03.09.2010 06:07:34 UPS: Bypass not in range; low voltage. 0x020F
03.09.2010 06:20:02 UPS: Bypass not in range; low voltage. 0x020F
03.09.2010 06:20:02 UPS: On battery power in response to rapid change of input. 0x0109
03.09.2010 06:32:18 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
03.09.2010 06:32:20 UPS: No longer on battery power. 0x010A
03.09.2010 08:58:17 UPS: Bypass not in range; low voltage. 0x020F
03.09.2010 08:58:17 UPS: On battery power in response to low input frequency. 0x0109
03.09.2010 08:59:33 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
03.09.2010 08:59:34 UPS: No longer on battery power. 0x010A
03.09.2010 09:00:03 UPS: Bypass not in range; low frequency. 0x020F
03.09.2010 09:00:03 UPS: On battery power in response to low input frequency. 0x0109
03.09.2010 09:00:03 UPS: No longer on battery power. 0x010A

03.09.2010 09:00:03 UPS: The output power is turned off. 0x0114

03.09.2010 09:00:04 UPS: A backfeed relay fault exists. 0x016B

03.09.2010 09:00:50 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
03.09.2010 09:01:20 UPS: Bypass not in range; low voltage. 0x020F
03.09.2010 09:05:27 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210

03.09.2010 09:42:48 UPS: A backfeed relay fault no longer exists. 0x016C

03.09.2010 09:43:00 UPS: The output power is now turned on. 0x0113

03.09.2010 09:43:09 UPS: Started a self-test. 0x0137
03.09.2010 09:43:17 UPS: passed via internal operation a self-test. 0x0105


Both Smart's are powered from independent power lines.
Both supply the critical blade-station (in its dirrerent PSes), and we want do the redundancy so!

I think this is not the wanted behavior of devices. As a customer we want the UPSes sustain many black-outs and change to battery power every time as needed, don't dropping the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now