Dear Sir,
At present I have one sever connected to the UPS by APC Network Management Card, now I want to added three more servers to the UPS for the graceful shutdown, what I did try to login the PowerChute Network Software by APC default user name and password it didn't accept it and then I try with domain administrator name and password it didn't accept again it try it with APC default username and password then it lock it then I unable to Login after some time I try with APC default user name and password I able to login when I click on configure the server or any other options nothing happens, then I try to do the garceful shutdown it works fine. My problem is I want to added three more servers to the UPS for the graceful shutdown. Could you please explain and the procedure what are the steps I have to take to make these three servers for graceful shutdown.Need your help.
Thanks in Advance.
Regards,E
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:59 PM . Last Modified: 2024-03-14 01:08 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:59 PM . Last Modified: 2024-03-14 01:08 AM
Ahmedmmd, just install the Power Chute Network Shutdown Software on other three Server. It will auto detect the configure Network Management Card on your network. Just select the same and install it on your network. So that you can graceful shutdown the connected servers in the event of power fail.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:58 PM . Last Modified: 2024-03-14 01:08 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:58 PM . Last Modified: 2024-03-14 01:08 AM
Hi Ahmed,
Since you already have the Network Management Card on your UPS and you have used the PowerChute Network Shutdown on the server connected on the UPS right now, all you need to do is to install the PowerChute Network Shutdown on the other 3 computers that you want to receive a graceful shutdown when UPS encounter any power events. Once you are done, you may check with your Network Management Card web interface under UPS>PowerChute>Clients, IP address of the computer that has Network Shutdown installed should be listed there.
Reference: Link: [Kbase 1141|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1141&p_created=1010390400&p...] Paragraph 4
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:59 PM . Last Modified: 2024-03-14 01:08 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:59 PM . Last Modified: 2024-03-14 01:08 AM
Ahmedmmd, just install the Power Chute Network Shutdown Software on other three Server. It will auto detect the configure Network Management Card on your network. Just select the same and install it on your network. So that you can graceful shutdown the connected servers in the event of power fail.