60 KVA UPS. Bypass out of tolerance alarm

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 60 KVA UPS. Bypass out of tolerance alarm
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Shaishav_shah
Shaishav_shah
Cadet

Posted: ‎2024-11-14 07:20 AM

0 Likes
1
316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-14 07:20 AM

60 KVA UPS. Bypass out of tolerance alarm

In my 60 KVA UPS, input voltage is 422, 426,433 volt, On display shown same but on UPS display bypass voltage showing 434, 458 and 453 volt and may be due to it alarm pop up bypass voltage out of tolerance and Bypass out of sync. What may be issue? What should be solution?

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-05 03:02 AM

1 Like
0
142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-05 03:02 AM

Hello,

 

It seems the unit is Easy 3M 60 KVA,we suggest to check the input voltage and frequency of mains then verify the below settings :

 

Min. bypass RMS voltage (V) default value  is -10V you can expand it to -15 V

Max. bypass RMS voltage (V)default value  is 10V you can expand it to 15V

Bypass frequency range (%) default value is 10 

Output slew rate (Hz/sec) is 0.5 Hz/s

 

The permissible three-phase voltage
- limit range is: -30%*Vnor ~ +25%*Vnor, the default range is -10%*Vnor~ +10%*Vnor (output voltage 400Vac)

 

for the frequency

 

Range is +/-10% (hysteresis :0.2Hz).

 

If all the setting are ok,then the bypass  SCRs needs to be verified and check they are not shorted, if yes the SCR KIT needs to be replaced if it is all ok,then replace the SCR driver board ,if the issue the same replace CT board and check if the readings are showing correct ,if the issue then control boards would required to be replaced

 

an SR is required to come onsite and verify the issue and check the logs for investigation 

 

Regards,

 

Karim

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-05 03:02 AM

1 Like
0
143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-05 03:02 AM

Hello,

 

It seems the unit is Easy 3M 60 KVA,we suggest to check the input voltage and frequency of mains then verify the below settings :

 

Min. bypass RMS voltage (V) default value  is -10V you can expand it to -15 V

Max. bypass RMS voltage (V)default value  is 10V you can expand it to 15V

Bypass frequency range (%) default value is 10 

Output slew rate (Hz/sec) is 0.5 Hz/s

 

The permissible three-phase voltage
- limit range is: -30%*Vnor ~ +25%*Vnor, the default range is -10%*Vnor~ +10%*Vnor (output voltage 400Vac)

 

for the frequency

 

Range is +/-10% (hysteresis :0.2Hz).

 

If all the setting are ok,then the bypass  SCRs needs to be verified and check they are not shorted, if yes the SCR KIT needs to be replaced if it is all ok,then replace the SCR driver board ,if the issue the same replace CT board and check if the readings are showing correct ,if the issue then control boards would required to be replaced

 

an SR is required to come onsite and verify the issue and check the logs for investigation 

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of