Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
60 KVA UPS. Bypass out of tolerance alarm
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-1407:20 AM
60 KVA UPS. Bypass out of tolerance alarm
In my 60 KVA UPS, input voltage is 422, 426,433 volt, On display shown same but on UPS display bypass voltage showing 434, 458 and 453 volt and may be due to it alarm pop up bypass voltage out of tolerance and Bypass out of sync. What may be issue? What should be solution?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-0503:02 AM
Hello,
It seems the unit is Easy 3M 60 KVA,we suggest to check the input voltage and frequency of mains then verify the below settings :
Min. bypass RMS voltage (V) default value is -10V you can expand it to -15 V
Max. bypass RMS voltage (V)default value is 10V you can expand it to 15V
Bypass frequency range (%) default value is 10
Output slew rate (Hz/sec) is 0.5 Hz/s
The permissible three-phase voltage - limit range is: -30%*Vnor ~ +25%*Vnor, the default range is -10%*Vnor~ +10%*Vnor (output voltage 400Vac)
for the frequency
Range is +/-10% (hysteresis :0.2Hz).
If all the setting are ok,then the bypass SCRs needs to be verified and check they are not shorted, if yes the SCR KIT needs to be replaced if it is all ok,then replace the SCR driver board ,if the issue the same replace CT board and check if the readings are showing correct ,if the issue then control boards would required to be replaced
an SR is required to come onsite and verify the issue and check the logs for investigation
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-0503:02 AM
Hello,
It seems the unit is Easy 3M 60 KVA,we suggest to check the input voltage and frequency of mains then verify the below settings :
Min. bypass RMS voltage (V) default value is -10V you can expand it to -15 V
Max. bypass RMS voltage (V)default value is 10V you can expand it to 15V
Bypass frequency range (%) default value is 10
Output slew rate (Hz/sec) is 0.5 Hz/s
The permissible three-phase voltage - limit range is: -30%*Vnor ~ +25%*Vnor, the default range is -10%*Vnor~ +10%*Vnor (output voltage 400Vac)
for the frequency
Range is +/-10% (hysteresis :0.2Hz).
If all the setting are ok,then the bypass SCRs needs to be verified and check they are not shorted, if yes the SCR KIT needs to be replaced if it is all ok,then replace the SCR driver board ,if the issue the same replace CT board and check if the readings are showing correct ,if the issue then control boards would required to be replaced
an SR is required to come onsite and verify the issue and check the logs for investigation