The importance of system time synchronization for accurate power values
Viewing external system data
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
When you have configured system integration correctly, IT Advisor retrieves accurate and up-to-date power measurements from the external system, such as Data Center Expert.
The IT Advisor and Data Center Expert servers can be physically positioned in different time zones. The system integration handles the time difference. However, both servers must be configured to synchronize time with the same NTP server:
Server
Time Synchronization Settings
IT Advisor
In the server's Webmin interface, IT Advisor > Setup
Data Center Expert
In System > Server Administration Settings > Time Settings
Otherwise, the retrieved power measurements may be out of sync:
Server Time
Consequence
IT Advisor ahead of Data Center Expert
No measured peak data retrieved
IT Advisor behind Data Center Expert
Incorrect measured peak data retrieved (out of sync)
For further instructions on how to configure system time synchronization for the Data Center Expert server, see the Data Center Expert documentation for Time settings.