Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Warning UPS Events

UPS Events

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • SmartConnect
  • UPS monitoring
  • UPS Events
  • Warning UPS Events
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Event Types
  • Critical UPS Events
  • Warning UPS Events
  • Informational UPS Events
  • Event Types
  • Critical UPS Events
  • Warning UPS Events
  • Informational UPS Events

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

SmartConnect Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to UPS Events
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
289081 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Warning UPS Events

Commander CDiggin Commander
‎2024-03-14 10:03 AM

Last Updated: Lt. Commander LFleming Lt. Commander ‎2024-11-04 03:36 AM

A Warning event is an event that requires attention. These events are displayed in the Event Log page of the Web Portal.

 

Warning UPS Events

  • Battery End of Life Exceeded
  • Battery Needs Replacement
  • Site Wiring Fault
  • UPS Command (Reboot) Unsuccessful
  • UPS Firmware Version Out of Date
  • UPS On Battery
  • User Initiated Bypass
Event Description Action
Battery End of Life Exceeded

The predicted lifespan of the UPS battery has expired.

NOTE: This is a Lifecycle Event

You must buy a replacement UPS battery. Visit www.apc.com or your reseller partner. If configured, your reseller will be notified when your UPS battery is due to expire.
Battery Needs Replacement

The Web Portal has detected that the UPS battery has reached its end of life. The UPS battery should be replaced immediately.

NOTE: This is a Lifecycle Event

You must buy a replacement battery cartridge immediately. Visit www.apc.com or your reseller partner. If configured, your reseller will be notified when your UPS battery is due to expire.
Site Wiring Fault
The UPS has detected that one of the following problems exist in the building wiring that supplies its input power:
• The input power to the UPS has its polarity reversed.
• The input power is not grounded, or the UPS is not properly grounded.
• The neutral wire of the input power source is overloaded (greater than 7 volts).
Have a licensed electrician investigate and correct the wiring issue.
UPS Command (Reboot) Unsuccessful
The UPS device’s outlet group(s) could not be completed at this time. For example, APC Smart-UPS could not contact the UPS or the UPS rejected the reboot request. If there is already a reboot in progress, the new reboot request will be unsuccessful.
To retry rebooting your outlet group(s), click the Try Again button in the Control section in the UPS Status page.
UPS Firmware Version Out of Date
The current UPS firmware is out of date, and a new firmware upgrade is available for your UPS. 
NOTE: A valid Standard or Advanced plan is required to initiate a UPS firmware upgrade via the Web Portal. 
NOTE: This is a Lifecycle Event

In the Web Portal, go to the Dashboard, click View UPS next to the UPS with a status description of "UPS Firmware Version Out of Date". In the UPS Status page, click the Active Events banner to expand the events, and click View Upgrade for more information, and to initiate the upgrade.

Alternatively, you can upgrade your UPS firmware via the LCD or using the Firmware Upgrade Wizard.

UPS On Battery
The UPS has switched to battery power to support its load in response to an input power issue, e.g. a power outage.
The devices connected to the UPS are supported by the UPS battery. Check the On Battery field displayed on the UPS Status page to see the runtime remaining. If the devices connected to the UPS are managed by PowerChute, they will be gracefully shut down according to the PowerChute configuration.
User Initiated Bypass
You have used the UPS bypass switch or a PowerChute Serial Shutdown diagnostic to put the UPS into bypass mode for maintenance.
While in bypass, the battery is not supporting the load. If a power outage occurs, the devices connected to the UPS are not protected by the UPS battery. When maintenance is completed, return the UPS to on line operation immediately.

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore