Hello
I want to replace old broken device MTN6725-0001 fw1.3 (DALIControl IP 1 7307/1.0b) to new MTN6725-0001 fw3.1 DALIControl IP 1 (DCA7310/1.0)
I have found in document (KNX- DALI Gateway REG-K/1/16(64)/64/IP1-ETS Software Description (EN) (Version V7310/1.0) on page 30 that there is restore function. I see that i can't download ETS project into device.
How replacement should look like, do i need to start from zero?
Can i downgrade firmware in new gateway and download configuration form ETS?
When i try to program gateway from ets i get this:
KNX fault
- Labels:
-
Local App
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Piotr,
to "Can i downgrade firmware in new gateway and download configuration form ETS?"
YES, you can downgrade the device to FW-Version 1.3.9 (Link to FW). Then it is compatible with your current ETS/PlugIn Version.
Means after the downgrade you can reuse the KNX-Part.
Related to the DALI-Part. If you didnt saved the DALI-Information with the dedicated function in the PlugIn (handled with a file) before you need to do the DALI-Part again. So it is helpfull to make a backup of the DALI-Configuration when you use the FW-Versions with the PlugIn.
When you use the new FW in combination with the dedicated ETS-APP then the DALI-Information are directly stored within the ETS.
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Piotr,
to "Can i downgrade firmware in new gateway and download configuration form ETS?"
YES, you can downgrade the device to FW-Version 1.3.9 (Link to FW). Then it is compatible with your current ETS/PlugIn Version.
Means after the downgrade you can reuse the KNX-Part.
Related to the DALI-Part. If you didnt saved the DALI-Information with the dedicated function in the PlugIn (handled with a file) before you need to do the DALI-Part again. So it is helpfull to make a backup of the DALI-Configuration when you use the FW-Versions with the PlugIn.
When you use the new FW in combination with the dedicated ETS-APP then the DALI-Information are directly stored within the ETS.
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thank you for fast reply @Thomas_Rohde
If you didnt saved the DALI-Information with the dedicated function in the PlugIn (handled with a file) before you need to do the DALI-Part again
Gateway device must be online on DALI network to make this backup file, or it can be done offline?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Piotr,
if you have the backup file I think you can do it offline.
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Is it possible to switch a dali 0001 to dali pro secure device 0101 with the backup file of the old one.
Or do I need to reprogram all ?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello i have the same problem as Mr Piotr regarding the firmware.
Can you share the link again, please?
Aleksandar
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Domotiqa,
the database format of the MTN6725-0001 is totally different from the new model MTN6725-0101, therefore, unfortunately, you cannot use its backup file.
However, the new installation procedure now allows you to maintain the configuration created with an external tool, therefore, by selecting that option, you should be able to maintain the association of the ECGs in the DALI groups.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
yes 😉