Hello
I cant access the application page.
While I Ping to google.com, 8.8.8.8 and all success
Also I have another SL on the same network and could access the application page, and both have the same DNS Settings!
What could be the issue?
- Labels:
-
SpaceLYnk
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello IC-Systems,
it should work with both FW-Versions but it can happen from time to time that it "for what ever reason" will not work.
This is then not general issue just appearing from one minute to the other.
How to go on:
- If there is a certain reason why you stick to FW2.6 then please try later again to reach the market place.
- If there is no certain reason just make the update to FW2.7 and check again (just a trial)
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello IC-Systems,
different Firmware? Really the same settings ... no typo or similar?
Can you share the network- settings (picture)?
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Thomas_Rohde
I Sent You screen Shot for network settings.
While one (working application) in version 2.7.0, the other in version 2.6.0
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello IC-Systems,
the network settings looks good. Which device has which FW and which is not running as expected?
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello IC-Systems,
it should work with both FW-Versions but it can happen from time to time that it "for what ever reason" will not work.
This is then not general issue just appearing from one minute to the other.
How to go on:
- If there is a certain reason why you stick to FW2.6 then please try later again to reach the market place.
- If there is no certain reason just make the update to FW2.7 and check again (just a trial)
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
i have the same problem and i upgrade firmware to 2.8 but i have the same problem?
what should I do?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Amr-LSEGYPT,
you mean that you cannot load application list, while having internet access on SL ... right?
What have you done to clearly be sure that you have internet access on your SL?
Are you working with DHCP or a fixed IP? In case of fixed IP ... did you set all necesarry entries like Gateway IP and DNS-Server1&2?
Only when these settings are correct, W4K/SL can have a proper access to the internet.
Please share/check your settings.
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I set all setting
IP and gateway and DNS 1,2
Same problem
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Amr-LSEGYPT,
can you check if you can reach google.com or 8.8.8.8 by the use of the network utilities?
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Network unreachable
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
IP 192.168.0.10
255.255.255.0
192.168.0.0
8.8.8.8
8.8.4.4
Same to my laptop with different range of IP
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Amr-LSEGYPT,
to be honest I am not a network specialist but I wonder about your gateway address with 192.168.0."0".
I think I have never seen "0" at the end only "1"?! Anyhow ...
What do you mean with "Same to my laptop with different range of IP"?
Do you mean only that you have a different IP-Address of your PC?
How big is your network? Is there maybe a router in between blocking?
Can you maybe take the SL into a little test-network?
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I mean IP for my PC is
192.168.0.100
255.255.255.0
192.168.0.1
IP for my wiser is
192.168.0.10
255.255.255.0
192.168.0.1
DNS1
8.8.8.8
I used hotspot wifi to let my PC have a network and I connect my Spacelynk to my laptop direct
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Just to understand your network correctly ...
You have a setup like this where your mobile provides the internet by working as a hotspot?
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I tried to use router and I connect my laptop to router port and Spacelynk to another one port
And I did all configuration but I have the same error when trying to load the list
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Just for me to understand correctly. You have architecture 1 or 2?
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Solved Thanks
It turns out that it was a problem with the firewall
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Super!
Thomas
Application Design Engineer