Automation Server missing from Server list (folder)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Automation Server missing from Server list (folder)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
3273 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Automation Server missing from Server list (folder)

Picard RobertAndriolo Picard
‎2024-06-04 09:17 PM

Issue

The automation server was added successfully; however, it never appeared in the server list. It did, however, get added to the communications tab.

The System Tree server list varies from the Communication tab list of servers.

No servers shown under "Servers" List in System Tree but is seen in Communications tabNo servers shown under "Servers" List in System Tree but is seen in Communications tab

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server

Cause

This is typically caused by the Group account not having permission to access the root path.  To verify this is the issue, log in with the "admin" user account and verify that the server lists match.

  

Looking at the screenshot below:

  1. If the Add (+ icon) option has been used to add the ES-1 Path Permissions, no server will be visible.  Additional Path Permissions need to be added for each server.
  2. If the Add System (Hierachial icon) option is used (the default for the local admin account group), this is the System's top-level path. Then, all servers will be seen.     

PermissionsTab.png

 See online WebHelp topic User Account Group – Software Permissions Tab

Resolution

Depending on which method is required by the end user.

  1. If using the Add (+icon) option
    1.  Login into the Enterprise Server with the local admin account
    2. Navigate to the Group(s) that need access to the server list and select the Permissions tab
    3. Add (+) the Automation Server(s) to the path permissions as shown below:
      PermissionsTab-1.png
    4. Repeat the above step for every server
    5. Each time a new Automation Server is added, repeat all steps. 
  2. If using the Add System (Hierachial icon) option
    1. Login into the Enterprise Server with the local admin account
    2. Navigate to the Group(s) that need access to the server list and select the Permissions tab
    3. Add System (Hierachial icon) to the path permissions as shown below:
      PermissionsTab-2.png
  3. Users must log off and log on to see any of the implemented changes.  

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore