Additional heating stage cyclically turning off
Hello!
I'm using the Valve Drive Controller to Control basic and additional heating.
I figured out that I have an issue with the Cycle time for automatic transimission parameter.
Every time I set the setpoint high enouht to power on the additional stage - It works until the Cycle time for automatic transmission passes. Then the Additional stage receives a '1' and a "0" right after. After that the additional stage remains switched off. Basic stage working perfectrly fine.
Now I've switched off the Cycle time for automatic transimission and the system is running well, but I know that I'm messing up with something.
Link copied. Please paste this link to share this article on your social media post.
2024-11-2002:39 AM
Hi KisevcompanyLTD! Sorry for the late reply! Can you provide more details (Telegram log) in order to see clearly what happens and what are the dedicated temperatures.