Which cable for ATV71 programming

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Which cable for ATV71 programming
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Altivar Process (Low Voltage)

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
FIlius
Crewman FIlius
Crewman

Posted: ‎2025-05-21 11:13 PM

0 Likes
5
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-21 11:13 PM

Which cable for ATV71 programming

Hello,

 

which type of cable do I need for programming ATV71?

 

Thank you.

Labels
  • Labels:
  • Contactors & Motor Starters
  • Drives & Motor Control
  • Low Voltage AC Drives
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2025-05-25 11:38 PM

0 Likes
0
994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-25 11:38 PM

Hi, Normal ethernet cable did only work if your ATV71 drive is adapted with an Ethernet Communication card. The port on the picture is the Modbus RTU (RS485) Can Port. It use a RJ45 connector, but is not Ethernet. You could use the cable TCSMCNAM3M002P. You could also try an alternative USB/RS485 adapter to connect. The RS485 is on pin4 and pin5 of the RJ45 connector. To use the dedicated cable is mostly the fastes and easiest way.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Everton_Souza
Ensign Everton_Souza Ensign
Ensign

Posted: ‎2025-05-26 04:49 AM

0 Likes
0
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-26 04:49 AM

Hi

The recommended cable for programming via Somove for the ATV71 is the TCSMCNAM3M002P.

The ATV71 has native Modbus RTU and CanOpen.

To be able to parameterize by Ethernet, the drive must have an optional MOdbus TCP/Ethernet IP board. In other words, it is not possible to commission using Somove via an Ethernet cable natively, the drive must be using an Ethernet board for this (e.g. VW3A3310D, VW3A3316).

The recommended cable would be the TCSMCNAM3M002P to use the drive's native Modbus RTU communication.

PS: It should also be possible to use a USB Can converter such as PCAN-USB adapter, but as I said, we recommend using the TCSMCNAM3M002P for drives that do not have an optional Ethernet board.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2025-05-22 11:53 PM

0 Likes
0
1039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-22 11:53 PM

Several possibilities are possible for programming ATV :

  • Through keypad, directly connected to Drive itself
  • Through SoMove, the freeware to be downloaded with also the ATV71 DTM, in this case you can use a simple Ethernet cable or it is also possible through the cable reference TCSMCNAM3M002P.
Bruno Jacqz, Drives training leader
Reply

Link copied. Please paste this link to share this article on your social media post.

FIlius
Crewman FIlius
Crewman

Posted: ‎2025-05-24 01:58 PM

0 Likes
0
995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-24 01:58 PM

I tried connecting with normal ethernet cable, but without luck.

On ATV71 it says "modbus/CANopen". That workd with normal ethernet cable?

What am I doing wrong, that I have problem with

1000016788.jpg

 

connection.

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2025-05-25 11:38 PM

0 Likes
0
995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-25 11:38 PM

Hi, Normal ethernet cable did only work if your ATV71 drive is adapted with an Ethernet Communication card. The port on the picture is the Modbus RTU (RS485) Can Port. It use a RJ45 connector, but is not Ethernet. You could use the cable TCSMCNAM3M002P. You could also try an alternative USB/RS485 adapter to connect. The RS485 is on pin4 and pin5 of the RJ45 connector. To use the dedicated cable is mostly the fastes and easiest way.

Reply

Link copied. Please paste this link to share this article on your social media post.

Everton_Souza
Ensign Everton_Souza Ensign
Ensign

Posted: ‎2025-05-26 04:49 AM

0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-26 04:49 AM

Hi

The recommended cable for programming via Somove for the ATV71 is the TCSMCNAM3M002P.

The ATV71 has native Modbus RTU and CanOpen.

To be able to parameterize by Ethernet, the drive must have an optional MOdbus TCP/Ethernet IP board. In other words, it is not possible to commission using Somove via an Ethernet cable natively, the drive must be using an Ethernet board for this (e.g. VW3A3310D, VW3A3316).

The recommended cable would be the TCSMCNAM3M002P to use the drive's native Modbus RTU communication.

PS: It should also be possible to use a USB Can converter such as PCAN-USB adapter, but as I said, we recommend using the TCSMCNAM3M002P for drives that do not have an optional Ethernet board.

Reply

Link copied. Please paste this link to share this article on your social media post.

FIlius
Crewman FIlius
Crewman

Posted: ‎2025-06-12 10:58 AM

0 Likes
0
748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-12 10:58 AM

Thank you. It works with TCSMCNAM3M002P cable. I was confused because in manual and our dealer said that I can use normal ethernet cable. Probably he didn't know that ATV71 has different connection types.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore