Posted: 2025-06-02 06:44 AM
Dear,
I need help to configure an ATS480 for inside Delta start.
I tried to start but i always have the fault change 123 to 231. (i make the change on the input wires but the fault remains)
My configuration is with main contactor. ( I set R3 to mains contactor ).
Start - Stop on start stop inputs, Reset on DI3.
R2 is set by it self on bypass contactor.
I also attached the somove file.
Can you please give me an advice what might be wrong. It is important to have a fast reply.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 01:27 AM
What is important on this type of wiring is to follow the right cabling (wire to wire) from the user's manual. Do not reverse any of them, it will create a fault...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 01:27 AM
What is important on this type of wiring is to follow the right cabling (wire to wire) from the user's manual. Do not reverse any of them, it will create a fault...