Hello,
During commissioning of a 315kW ATV660 drive, I've measured the incomming current.
The 3 phase currents have not the same value L1= 580A, L2=565A, L3= 575A.
Is this problematical ? How can advice ?
Thank you for your kind advice!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-04-16 04:02 AM
This is an unbalance of 15A between L1 and 2 (2,5%). Such a behavior is indicating,
that the 3 phase incoming voltage is slightly different or distorted. You can check
with an oscilloscope the voltage waveform, verisimilar the voltage is distorted
slightly on it´s top. Could be caused by some nonlinear loads which emits a 3rd rank harmonic.
But anyway, don’t worry this is not a problem for the drive itself.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-04-16 04:02 AM
This is an unbalance of 15A between L1 and 2 (2,5%). Such a behavior is indicating,
that the 3 phase incoming voltage is slightly different or distorted. You can check
with an oscilloscope the voltage waveform, verisimilar the voltage is distorted
slightly on it´s top. Could be caused by some nonlinear loads which emits a 3rd rank harmonic.
But anyway, don’t worry this is not a problem for the drive itself.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.