Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Unsymmetrical incoming current on frequency inverter

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Re: Unsymmetrical incoming current on frequency inverter
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
BJacqz Mentor
49
LeoLazzaro
LeoLazzaro Troubleshooter
16
PriscilaCunha22
PriscilaCunha22 Troubleshooter
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Altivar Process (Low Voltage)

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-04-16 02:11 AM

3 Likes
2
2748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-16 02:11 AM

Unsymmetrical incoming current on frequency inverter

Hello,

 

During commissioning of a 315kW ATV660 drive, I've measured the incomming current.

 

The 3 phase currents have not the same value L1= 580A, L2=565A, L3= 575A.

 

Is this problematical ? How can advice ?

 

Thank you for your kind advice!

 

 

Labels
  • Labels:
  • Training & How to
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ReinhardK
ReinhardK Contributor
Contributor

Posted: ‎2021-04-16 04:02 AM

1 Like
1
2737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-16 04:02 AM

This is an unbalance of 15A between L1 and 2 (2,5%). Such a behavior is indicating,
that the 3 phase incoming voltage is slightly different or distorted. You can check
with an oscilloscope the voltage waveform, verisimilar the voltage is distorted
slightly on it´s top. Could be caused by some nonlinear loads which emits a 3rd rank harmonic.
But anyway, don’t worry this is not a problem for the drive itself. 

See Answer In Context

  • Tags:
  • english
  • harmonic
  • THDi
  • THDu
  • unbalance line current
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
ReinhardK
ReinhardK Contributor
Contributor

Posted: ‎2021-04-16 04:02 AM

1 Like
1
2737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-16 04:02 AM

This is an unbalance of 15A between L1 and 2 (2,5%). Such a behavior is indicating,
that the 3 phase incoming voltage is slightly different or distorted. You can check
with an oscilloscope the voltage waveform, verisimilar the voltage is distorted
slightly on it´s top. Could be caused by some nonlinear loads which emits a 3rd rank harmonic.
But anyway, don’t worry this is not a problem for the drive itself. 

  • Tags:
  • english
  • harmonic
  • THDi
  • THDu
  • unbalance line current
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-05-05 12:40 AM

In response to ReinhardK
0 Likes
0
2644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-05 12:40 AM

Thank you @ReinhardK , this was very useful.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore