The Altivar Process ATV 630 has the possibility to manage several motors on a pumping system.
The final objective is to get and keep a constant pressure at the output of booster station.
See some more information through FAQ, and a movie available on Youtube on the subject.
https://www.se.com/ww/en/faqs/FA299545/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 04:54 AM
Altivar Process ATV630 is able to monitor a complete boosting installation thanks to the internal feature MultiDrives Link.
This allows a simple way to connect all the drives on the same network (Ethernet).
This way of connection highly facilitate the cabling (compared to other systems using Inputs Outputs individually.
The product ATV630 allows to monitor up to 6 pumps. It is possible also to have one master or eventually one other master as redundant (in case the first master needs some maintenance actions for example). This is done to ensure continuity of service for the system.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-06 06:02 AM . Last Modified: 2021-07-07 06:08 AM
Interesting information, Bruno, and I have an additional question: how many motors/pumps can you manage with Altivar ATV630?
Thank you in advance for your answer.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 04:54 AM
Altivar Process ATV630 is able to monitor a complete boosting installation thanks to the internal feature MultiDrives Link.
This allows a simple way to connect all the drives on the same network (Ethernet).
This way of connection highly facilitate the cabling (compared to other systems using Inputs Outputs individually.
The product ATV630 allows to monitor up to 6 pumps. It is possible also to have one master or eventually one other master as redundant (in case the first master needs some maintenance actions for example). This is done to ensure continuity of service for the system.
Link copied. Please paste this link to share this article on your social media post.