Altivar 31 pump control, current surging
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-05 05:17 AM
Despite this is an old request, let me give some explanation. First point is to ensure the motor name plate has been well set in the drive settings (I means motor data such as power (or cos phi), speed, current,...) as indicated in the user's manual (see document joined). Another possibility is to share the soMove configuration file in your post, that would be helpful for analysis. In addition, electrical drawings of your installation would be helpfull too.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-05 05:17 AM
Despite this is an old request, let me give some explanation. First point is to ensure the motor name plate has been well set in the drive settings (I means motor data such as power (or cos phi), speed, current,...) as indicated in the user's manual (see document joined). Another possibility is to share the soMove configuration file in your post, that would be helpful for analysis. In addition, electrical drawings of your installation would be helpfull too.