Posted: 2023-11-16 03:44 AM
ATV630 Bacnet IP
Does Schneider Electric have a communication solution for ATV630 Bacnet IP? Thanks.
- Labels:
-
Low Voltage AC Drives
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-16 12:36 PM
Schneider Electric did not offer any Drive which support BACnet IP. For ATV6xx you could use the follow Communication Card to use BACnet MS/TP VW3A3725. ATV212 offers directly BACnet MS/TP.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-17 05:40 AM
Thank you for the question
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-16 11:54 PM
Hello Pablo,
Bacnet IP is communication device for Building then the ATS212 is the Altivar for Building, and this type of communication is available in this product...
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-16 12:36 PM
Schneider Electric did not offer any Drive which support BACnet IP. For ATV6xx you could use the follow Communication Card to use BACnet MS/TP VW3A3725. ATV212 offers directly BACnet MS/TP.
Link copied. Please paste this link to share this article on your social media post.