ATV320 drive
What is a SCF3 fault on a ATV320 drive?
  • Low Voltage AC Drives
Lauryn_Cossard
Lt. Commander Lauryn_Cossard Lt. Commander
Lt. Commander
Posted: ‎2024-11-20 12:23 AM
This is a ground Short Circuit fault.
Recheck all the motor parameters. Check all the cables connecting the drive to the motor, and the motor insulation. Reduce the switching frequency. Check the adjustment of speed loop and/or brake, if applicable. Increase the Time to Restart ( ttr parameter in Set menu) - if there is a brake?  Disconnect the motor leads and then turn off the OPL and try to run the drive open circuit and see if it still faults.  If it does, the drive appears to be inoperative
BJacqz
Commander
Posted: ‎2024-11-20 12:52 AM
In addition to all, regarding Drives faults, I would advise you to have a look inside the programming manual, there are some slight explanation of possible cause and remedy
Bruno Jacqz, Drives training leader
Lauryn_Cossard
Lt. Commander
BJacqz
Commander