What is a SCF3 fault on a ATV320 drive?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-20 12:23 AM
Hello,
This is a ground Short Circuit fault.
Recheck all the motor parameters. Check all the cables connecting the drive to the motor, and the motor insulation. Reduce the switching frequency. Check the adjustment of speed loop and/or brake, if applicable. Increase the Time to Restart ( ttr parameter in Set menu) - if there is a brake? Disconnect the motor leads and then turn off the OPL and try to run the drive open circuit and see if it still faults. If it does, the drive appears to be inoperative
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-20 12:52 AM
In addition to all, regarding Drives faults, I would advise you to have a look inside the programming manual, there are some slight explanation of possible cause and remedy
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-20 12:23 AM
Hello,
This is a ground Short Circuit fault.
Recheck all the motor parameters. Check all the cables connecting the drive to the motor, and the motor insulation. Reduce the switching frequency. Check the adjustment of speed loop and/or brake, if applicable. Increase the Time to Restart ( ttr parameter in Set menu) - if there is a brake? Disconnect the motor leads and then turn off the OPL and try to run the drive open circuit and see if it still faults. If it does, the drive appears to be inoperative
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.