Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82247members
349809posts

Unable to resolve dependency 'EntityFramework'.

SmartConnector Forum

Discussion of SmartConnector applications for integration of various other building management systems (BMS) into EcoStruxure Building Operation

Solved
David_Glasgow
Ensign Ensign
Ensign
0 Likes
1
516

Unable to resolve dependency 'EntityFramework'.

When installing the Mongoose.Process, I get the following errors:

Restoring packages for C:\Users\SESA44648\source\repos\SmartConnecterWeatherSamples\SmartConnector.FirstWeatherExtension\SmartConnector.FirstWeatherExtension.csproj...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/mong...
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/mong... 202ms
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/mong...
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/mong... 1689ms
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/newt...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/syst...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ews....
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ews....
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/mong...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/sxl....
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/newt... 230ms
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ews.... 298ms
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ews....
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/sxl.... 355ms
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/sxl....
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ews.... 472ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/syst... 967ms
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/owin...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/weba...
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ews.... 1160ms
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ews....
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/mong... 1199ms
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/mong...
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 197ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/owin... 209ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 281ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 312ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/weba... 356ms
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ews.... 431ms
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/sxl.... 1367ms
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/nlog...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/nlog...
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/nlog... 190ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/nlog... 195ms
OK https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/mong... 948ms
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/enti...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ncro...
GET https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/swas...
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/enti... 213ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 216ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 265ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 310ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 316ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 344ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 366ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 411ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 416ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 465ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 463ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/micr... 505ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/swas... 514ms
NotFound https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/flatcontainer/ncro... 550ms
Installed SxL.Common 2.5.4.18 from https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/index.json with content hash VjpDrSVRyu1x9EhDao94dMhTrUTmULHNCoGlttpJE8IlbD27Rm23f7MKUvruwDQhMIEYrnB0KKDnc/nPO4sxwg==.
Installed Mongoose.Common 2.5.4.18 from https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/index.json with content hash 0woa7MbkEGLvvv+kC9pLDVCuWSwsf/Yt0cYRksLEVLTItVKZ/bbaua+5A4uMJiRH0OY5wq3ZRSvXeXS2vUwBaQ==.
Installed Ews.Common 2.5.4.18 from https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/index.json with content hash 4qoPeVV+gbOFe4/Omjv6lBhEo1AC4H1MO3IC+N74gnBQXVN1wsXAaDOD4h5NDkD5vVu0KuXf2hQ8eWKuIln3GA==.
Installed Ews.Client 2.5.4.18 from https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/index.json with content hash XKHiQoZWjflPsUxh7ZQyHbx3WxwuLkgZUr8OIMWzTes8uHj+SlfaqibbyOlCfFWmZoG5yIsJCdR2fNG45o9IfA==.
Installed Mongoose.Process 2.5.4.18 from https://www.myget.org/F/mongoose/auth/2dd53f27-71f5-455d-b624-c3f71cad5547/api/v3/index.json with content hash oGOLFF9GKRB4K/MQBw4KOWrVn8U/MZXgoqmBHPmC/kOxhLoJ98R8j5UK6j0uUc/BDONlJQ3P1nOv5GNz+fD0Gg==.
NU1102: Unable to find package Newtonsoft.Json with version (>= 12.0.2)
- Found 1 version(s) in Microsoft Visual Studio Offline Packages [ Nearest version: 9.0.1 ]
- Found 0 version(s) in SmartConnector
NU1101: Unable to find package System.ValueTuple. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.AspNet.WebApi.Client. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.AspNet.WebApi.Core. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.Owin. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Owin. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package WebApiThrottle.StrongName. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package EntityFramework. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.AspNet.Cors. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.AspNet.Identity.Core. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.AspNet.Identity.Owin. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.AspNet.WebApi.Owin. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.AspNet.WebApi.OwinSelfHost. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.Owin.Cors. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.Owin.Host.HttpListener. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.Owin.Hosting. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.Owin.Security. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.Owin.Security.Cookies. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Microsoft.Owin.Security.OAuth. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package NCrontab.Signed. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package Swashbuckle.Core. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package NLog.Targets.Syslog. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
NU1101: Unable to find package NLog. No packages exist with this id in source(s): Microsoft Visual Studio Offline Packages, SmartConnector
Time Elapsed: 00:00:06.7463374
========== Finished ==========

 

 

Tags (1)

Accepted Solutions
David_Glasgow
Ensign Ensign
Ensign
0 Likes
0
487

Re: Unable to resolve dependency 'EntityFramework'.

I added "https://api.nuget.org/v3/index.json" to the Package sources and it seems to work now.

 
 

 

 

See Answer In Context

Tags (1)
1 Reply 1
David_Glasgow
Ensign Ensign
Ensign
0 Likes
0
488

Re: Unable to resolve dependency 'EntityFramework'.

I added "https://api.nuget.org/v3/index.json" to the Package sources and it seems to work now.

 
 

 

 

Tags (1)