SmartConnector Forum
Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.
Link copied. Please paste this link to share this article on your social media post.
Lately when I developing an extension and I try to acknowledge the alarm events of SBO, it always tells PERMISSION_DENIED ,I am not sure any configuration incorrect.
For example when I try to acknowledge alarm event as:
{ "AlarmId": "02/Server 1/Test/OverTemp", "Acknowledgeable": 1, "OccurredOn": "2017-06-07T14:07:36Z", "LastTransitionedOn": "2017-06-08T00:07:08Z", "Message": "The room temp is too low", "Priority": 100, "State": 1, "Type": "GeneralAlarm", "Id": "/Server 1|/Server 1/Test/OverTemp|4c7f52bb-5450-41f9-9387-4a260242d023" },
And I recall the GUID of the alarm is the ID to be used for acknowledgement, then I use the Id=4c7f52bb-5450-41f9-9387-4a260242d023 to acknowledge this alarm, the response will be as:
{ "Message": "PERMISSION_DENIED" }
The SBO endpoint and credential is all correctly.
---Austen
Link copied. Please paste this link to share this article on your social media post.
I have figure it out, I should use Id="%2FServer%201%7C%2FServer%201%2FTest%2FOverTemp%7C11873d28-6e3c-4d03-8f8c-7f8d01e6e495" to acknowledge the alarm of my example.
Thanks.