EWS Unit percent (%) not recognized by SBO

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • EWS Unit percent (%) not recognized by SBO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
Start a Topic
MichelJansson
Lieutenant MichelJansson Lieutenant
Lieutenant

Posted: ‎2017-05-16 02:11 AM

0 Likes
5
1181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-16 02:11 AM

EWS Unit percent (%) not recognized by SBO

Hi,

I'm not sure if this is a SBO issue or a connector issue. Anyhow, after completing the sample project, I see that units containing % symbol, i.e. '%' or '% Rh', is not recognized by SBO and the values just shows up with no unit.

Do we need to escape the symbols, or is there something else going on with my specific project?

I'm using VS2017, SBO 1.9.1.95 and the latest connector.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2017-05-16 06:46 AM

0 Likes
4
1144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-16 06:46 AM

Michel,

Please correct me if my assumption below is incorrect.  From your question I infer SBO is the EWS Client and you have entered ValueItems into a SmartConnector with Unit value that contains the % character.  Under this scenario, you do not need to escape anything.

The list of acceptable ValueItem Unit values are listed in Table 101 of the EcoStruxure Web Services Specification (you can access that on the SmartConnectorServer Download Center or the Featured Content of this forum site).  In looking in that table, I don't see Relative Humidity listed (although it should be).  The proper value for that should be %RH (no space, both letters capitalized).

I confirmed that %RH does work with SBO (we tested 1.8 and 1.9).  However, I did encounter more SBO EWS Client "weirdness" in doing this testing.  If you edit the point in SmartConnector, SBO does NOT always show the proper property values in the Hardware folder; you will need to re-host the point to get the update. 

Let me know if you have any further issues on this.

Reply
MichelJansson
Lieutenant MichelJansson Lieutenant
Lieutenant

Posted: ‎2017-05-18 01:37 AM

0 Likes
2
1144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-18 01:37 AM

Mark,

Yes, SBO is consuming the SmartConnector value items as per your sample project (SmartConnector WeatherExtension).

Right out of the box, using your project, % unit is not displayed in SBO. But I also note that % unit is not in table 102, that cannot be right.

The reason for using '% Rh' was due to the fact that is how SBO writes it. I noticed that hPA in your project did not work, so I looked that up in SBO, and changed it to however SBO displayed it (hPa), and got that working.

Reply
MichelJansson
Lieutenant MichelJansson Lieutenant
Lieutenant

Posted: ‎2017-05-18 01:52 AM

0 Likes
0
1144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-18 01:52 AM

Actually, I can see now that SBO (1.9.1) does not even recognize the % unit of it's own EWS value items. Must be a SBO bug.

Reply
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2017-05-18 05:31 AM

0 Likes
1
1144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-18 05:31 AM

While SBO does show the unit as % Rh, in order for SBO to properly recognize it, the EWS server should send a unit value of %RH

Reply
MichelJansson
Lieutenant MichelJansson Lieutenant
Lieutenant

Posted: ‎2017-05-22 04:11 AM

0 Likes
0
1144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-22 04:11 AM

Roger.

Do you maybe have an answer regarding just the percent unit as well?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore