EBO Values' discovery takes long time

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • EBO Values' discovery takes long time
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-02-19 01:34 AM

0 Likes
2
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-19 01:34 AM

EBO Values' discovery takes long time

Hi,

We have a Discovery processor that discovers all values in the EBO and attached remote controllers. One of our customers has 30,000 defined values in 30 remote controllers.

It takes 9 hours for the Discovery processor to complete which is very long time.

 

We consider breaking the Discovery processor to 30 Discovery processor, one for each controllers. This way, the customer will be able to only start the processor where there are changes and not to wait again for 9 hours.

 

My questions are:

1. Is there a limit of the number of processors we can define?

2. Does the processors' names must be unique?

3. Can we set the 'Start Search At Root Container Item' as hidden field with a predefined value 'False' in our Discovery processor settings?

4. Can we enforce the user to define at least one item in "Folder to Scan" in our Discovery processor settings? 

 

Thank you.

 

Mike

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2021-02-19 10:08 AM

0 Likes
1
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-19 10:08 AM

Hi Michael,

 

In general I wouldn't recommend configuring 30 instances of the same processor just for a discovery as just this configuration of this alone will be time consuming!

 

If you are experiencing this level of slowness you may want to take a look at what the root cause of this is, as creating 30 processors, and hope they run in parallel may not work as you hope.

 

But to your questions:

 

1. Not hard coded, but if you want to run all 30 at once, you will need to increase the number of Worker Threads in the settings.

2. No the names do not need to be unique.

3. This is possible, take a look at the 'VisibleWhenAttribute' in chapter 9.4.8 of the Developers Guide

4. This is possible, take a look at the 'CollectionLengthAttribute' in chapter 9.4.1 Developers Guide.

 

Best Regards,

 

-Jeff

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2021-02-19 10:08 AM

0 Likes
1
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-19 10:08 AM

Hi Michael,

 

In general I wouldn't recommend configuring 30 instances of the same processor just for a discovery as just this configuration of this alone will be time consuming!

 

If you are experiencing this level of slowness you may want to take a look at what the root cause of this is, as creating 30 processors, and hope they run in parallel may not work as you hope.

 

But to your questions:

 

1. Not hard coded, but if you want to run all 30 at once, you will need to increase the number of Worker Threads in the settings.

2. No the names do not need to be unique.

3. This is possible, take a look at the 'VisibleWhenAttribute' in chapter 9.4.8 of the Developers Guide

4. This is possible, take a look at the 'CollectionLengthAttribute' in chapter 9.4.1 Developers Guide.

 

Best Regards,

 

-Jeff

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-02-23 10:39 AM

0 Likes
0
923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-23 10:39 AM

Hi Jeff,

 

Thank you. Understood.

 

Mike

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore