Help
  • Explore Community Expore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Explore Community Explore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • EcoStruxure Asset Advisor
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

EBO Discovery - AS-P point value called "Value"?

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • EBO Discovery - AS-P point value called "Value"?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
JeffBowman Schneider Alumni (Retired)
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
mike_meirovitz
Commander mike_meirovitz
21
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Building Operation

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Solved
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-06-13 07:55 AM

0 Likes
8
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-13 07:55 AM

EBO Discovery - AS-P point value called "Value"?

Hi,

During the discovery of the EBO values, the discovery finds a point/value inside the AS-P controller called "Value". See below:

11/9650KU0501_1000/Lon/Net/IO/M4/UC\8252GF262B000/Value

I don't see a point called "Value" in the Workstation. See the attached screen capture. 

 

In addition, the discovery finds the same point/value under "01". See below:

01/9650KU0501_1000/Lon/Net/IO/M4/UC\8252GF262B000

 

Can someone explain? What does "11" (in 11/9650KU0501_1000/Lon/Net/IO/M4/UC\8252GF262B000/Value) stands for?

 

Thank you.

 

Mike

  • Thumbnail of EcoStruxure™ Building Operation
    Schneider Electric
    EcoStruxure™ Building Operation
View products (1)
Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-06-15 09:09 AM

0 Likes
0
724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-15 09:09 AM

I just noticed in your logs:

 

2021-06-14 16:08:46.3352,Debug,EwsConsume,<no principal>,GetContainerItems,e92a9a76-bab0-4a81-8451-05390a390095,Response,{"GetContainerItemsItems":[],"GetContainerItemsErrorResults":[{"Id":"11/9650KU0501_1000/Program/UC","Message":"INVALID_ID"}],"GetContainerItemsStatus":null,"version":"1.2"}

 

You seem to have given it the wrong EWS ID. The prefix should be 00/, as "UC" is a container. From what I can see the right ID to use would be 00/9650KU0501_1000/Program/UC 

 

 

Sure. See attached. So I assume we should always use "00" prefix for all value items in folders.

 


No, 00 is for ContainerItem(e.g. folder), ValueItem is 01. 

 

Hope this solves your problem.

 

BR

Armend

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 8
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-06-13 10:33 PM . Last Modified: ‎2022-10-19 01:38 AM

0 Likes
7
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-13 10:33 PM

Hi,

 

Please take a look at this thread:

 

https://community.se.com/t5/SmartConnector-Forum/SmartConnector-codes-and-types/td-p/274479

 

This means "01/..." is the point(ValueItem) and "11/..." is a property of that ValueItem. "/Value" is just one of the properties a ValueItem can have.

 

Hope this helps.

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-06-14 01:54 AM

0 Likes
6
753
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-14 01:54 AM

Hi Armend,

 

Thank you for your answer. I saw this thread before. My question is:

 

If we set the "Folder To Scan" value to "00/9650KU0501_1000/Program/UC" in our SmartConnector extension discovery processor, what value items we should expect?

 

01/9650KU0501_1000/Program/UC/Value1

01/9650KU0501_1000/Program/UC/Value2

01/9650KU0501_1000/Program/UC/Value3

...

 

or:

11/9650KU0501_1000/Program/UC/Value1

11/9650KU0501_1000/Program/UC/Value2

11/9650KU0501_1000/Program/UC/Value3

 

Thank you.

 

Michael

 

@JeffBowman 

 

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-06-14 06:12 AM

0 Likes
5
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-14 06:12 AM

Hi,

 

One more question:

 

If the SmartConnector discovers an item as:

"11/9650KU0501_1000/Program/UC/8252GF262B000SNVT",

 

Can I use a folder name (in Folders To Scan) such as "00/9650KU0501_1000/Program/UC". When I try this I get th3 "INVALID_ID" response in the SmartConnector log file:

 

2021-06-14 16:08:46.3352,Debug,EwsConsume,<no principal>,GetContainerItems,e92a9a76-bab0-4a81-8451-05390a390095,Response,{"GetContainerItemsItems":[],"GetContainerItemsErrorResults":[{"Id":"11/9650KU0501_1000/Program/UC","Message":"INVALID_ID"}],"GetContainerItemsStatus":null,"version":"1.2"}

 

Any idea why?

 

Thanks.

 

Mike

 

@JeffBowman 

 

 

 

 

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-06-15 12:50 AM

0 Likes
4
741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-15 12:50 AM

Hi,

 

I tried this on my system and it seems to work fine.

 

Could you attach a screenshot of the system tree, showing the points and container you are trying to reach?

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-06-15 06:37 AM

0 Likes
3
734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-15 06:37 AM

Hi Armend,

Thank you for your answer.

We have one controller (9650KU0501_1000) connected in the EBO. See the attached screen capture. The discovery processor finds the controllers' values in two branches:

11/9650KU0501_1000
and
01/9650KU0501_1000

Can you explain why two branches are discovered for one controller? What is the difference between "11" and "01"?

Thanks.

Mike

Attachments
Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-06-15 08:04 AM

0 Likes
2
730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-15 08:04 AM

Hello,

 

Could you please expand the tree on the left so that the points we are talking about are visible? 

 

I do not know how your processor works so I can't know for sure but it seems like you are building the tree based on the EWS ID, including the first two digits. These are not part of the "path" but show what kind of node it is. 00 is a container etc.. as discussed in the thread mentioned above.

 

Hope this clears it up a bit.

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-06-15 08:36 AM

0 Likes
1
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-15 08:36 AM

Hi,

 

Sure. See attached. So I assume we should always use "00" prefix for all value items in folders.

 

Regards,

 

Mike

Attachments
Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-06-15 09:09 AM

0 Likes
0
725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-15 09:09 AM

I just noticed in your logs:

 

2021-06-14 16:08:46.3352,Debug,EwsConsume,<no principal>,GetContainerItems,e92a9a76-bab0-4a81-8451-05390a390095,Response,{"GetContainerItemsItems":[],"GetContainerItemsErrorResults":[{"Id":"11/9650KU0501_1000/Program/UC","Message":"INVALID_ID"}],"GetContainerItemsStatus":null,"version":"1.2"}

 

You seem to have given it the wrong EWS ID. The prefix should be 00/, as "UC" is a container. From what I can see the right ID to use would be 00/9650KU0501_1000/Program/UC 

 

 

Sure. See attached. So I assume we should always use "00" prefix for all value items in folders.

 


No, 00 is for ContainerItem(e.g. folder), ValueItem is 01. 

 

Hope this solves your problem.

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc