Hi All,
I am struggling a bit to get a DateTime filter going when using GET/TrendSamples.
What should the format be for this? I have tried a bunch of different formats however it keeps returning all the latest entries.
Parameter | Description | Parameter Type | Data Type |
alarmId | Return only AlarmEvent for the referenced Alarm. | Query | String |
trendId | The Id of the Trend which TrendSample are to be returned for. This parameter is not optional. | Query | String |
state | Return only TrendSample with this State value. | Query | Enumeration (See Table 1) |
sampleOnOrAfter | Return only TrendSample with SampleDate which is on or after this value. | Query | DateTime |
sampledBefore | Return only TrendSample with SampleDate which is before this value. | Query | DateTime |
orderBy | TrendSample will be returned in this order. SampleDateAscending by default. | Query | Enumeration SampleDateAscending=0 SampleDateDescending=1 |
take | Number of TrendSample that should be returned. 200 by default. | Query | Integer |
skip | Number of TrendSample that should be skipped before items are returned. 0 by default. | Query | Integer |
Link copied. Please paste this link to share this article on your social media post.
Any valid date format will work however, if your values do not include time zone offset or are not in UTC format, then the resulting predicate may not be what you intended.
Also, sampledOnOrAfter and sampledBefore can be used separately or in tandem. So each side of the following expression may be omitted if the supplied value is null.
TrendSample.SampleDate>= sampledOnOrAfter && TrendSample.SampleDate< sampledBefore
Some sample requests would be helpful in determining where the issue may be. If you are using the SOAP provider, you should enable "Ews Consume" filtering (Debug level) and you will see how your REST calls are translated into an EWS SOAP request.
Link copied. Please paste this link to share this article on your social media post.
Hi Mark,
Ok Using the time format 2017-05-09T22:00:07Z did the trick. However I have a concern on how Smart Connector is handling the timestamps on the samples.
In South Africa We are GMT+2. When I run the GET/TrendSamples request it reduces the actual timestamp by 2 hours and what makes it worse is if I have a midnight sample on 2017-05-10, it incorrectly gives me a timestamp of 2017-05-09 22:00PM.
Of course it is using UTC but there must be a way to get around this:
Link copied. Please paste this link to share this article on your social media post.
Petri,
All values returned by the REST Gateway should be in UTC. With the SoapEwsRestProvider, SmartConnector is passing the values through from the server since EWS mandates that the values returned are in UTC.
Before we can determine if this might be a serialization issue in the REST layer, we need to see what SBO is returning over SOAP.
Do you have any log captures with that information? If you enable "Ews Consume" logging filter at Debug level you will see the SOAP request/response pairs. If the value there is correct, but the value returned over REST is not, then we may have a serialization issue.