Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Customer cannot login localhost:8082
SmartConnector Forum
Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2023-09-1502:42 AM
Customer cannot login localhost:8082
Hi,
Customer Installed SmartConnector on their server and the portalpage does not load. He said that the service is in running state, but the login page do not respond.
2023-09-14 16:30:03.7451,Error,Service,<no principal>,Unable to load DLL 'SE.WorkStation.Licensing.LMClient32.dll': The specified module could not be found. (Exception from HRESULT: 0x8007007E)
at SE.WorkStation.Licensing.LMClient.Api.Managers.NativeMethods.License32.OpenSession()
at SE.WorkStation.Licensing.LMClient.Api.Managers.LicenseSystem.OpenSession()
at SE.WorkStation.Licensing.LMClient.Api.Services.LicenseService.SessionHandle()
at SE.WorkStation.Licensing.LMClient.Api.Services.LicenseService.Checkout(String feature, String version, Int32 quantity)
at Mongoose.Service.Licensing.LicenseEnforcer.HasValidFlexeraLicense()
,[],
But are those only because of the missing license? The license cannot be loaded if the portalpage do not respond...