Workbench Programs vs SCADAPack Programs - Local Variables

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • Workbench Programs vs SCADAPack Programs - Local Variables
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
RemoteConnect for the SCADAPack x70
product field
Schneider Electric
SCADAPack™ 47x | 47xi

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
infinityscott
Crewman infinityscott
Crewman

Posted: ‎2024-11-21 02:44 PM . Last Modified: ‎2024-11-21 03:09 PM

0 Likes
3
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-21 02:44 PM . Last Modified: ‎2024-11-21 03:09 PM

Workbench Programs vs SCADAPack Programs - Local Variables

Hi everyone,
 

In Workbench a Program can have Local Variables - these are consumed within the program 'POU' but are not available to anything outside of it.

 

Is this option available in SCADAPack x70 Logic - I couldn't see any way to do that...

Labels
  • Labels:
  • RTU
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2024-11-26 08:40 AM . Last Modified: ‎2024-11-26 08:44 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-26 08:40 AM . Last Modified: ‎2024-11-26 08:44 AM

Hello Scott,

 

The RemoteConnect Help guide offers assistance on this topic as well as many others, in the section called "Porting Guide for SCADAPack E to SCADAPack RemoteConnect" which is in the Configuration Manuals. Look at the specific topic called "Global and Local Variables".

 

Please refer to the two attached screen captures which will show more details. You'll see in one image that a Program Unit was created instead of a Section. Variables in a Program Unit are by default Private, though they can be changed to Input, Output or Public type.

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2024-11-26 08:40 AM . Last Modified: ‎2024-11-26 08:44 AM

0 Likes
0
1394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-26 08:40 AM . Last Modified: ‎2024-11-26 08:44 AM

Hello Scott,

 

The RemoteConnect Help guide offers assistance on this topic as well as many others, in the section called "Porting Guide for SCADAPack E to SCADAPack RemoteConnect" which is in the Configuration Manuals. Look at the specific topic called "Global and Local Variables".

 

Please refer to the two attached screen captures which will show more details. You'll see in one image that a Program Unit was created instead of a Section. Variables in a Program Unit are by default Private, though they can be changed to Input, Output or Public type.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

infinityscott
Crewman infinityscott
Crewman

Posted: ‎2024-11-27 09:12 AM

0 Likes
1
1356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-27 09:12 AM

Thanks Joel. 

 

This falls down to the difference between a Section and a Program Unit, which I find the manuals don't really explain anywhere - I had beena voiding Program Units but evidently need them. 

 

So, on a thus related note: the manuals state that a Program Unit can access Global Variables via the External setting. However, when I do this they are not connected. I don't want to pass everything in and out as parameters. Is this correct? They don't appear in the (Global) Variables...

Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2024-11-29 08:39 AM . Last Modified: ‎2024-11-29 08:43 AM

In response to infinityscott
0 Likes
0
1344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-29 08:39 AM . Last Modified: ‎2024-11-29 08:43 AM

Hi Scott,

 

I discussed this with our Logic Editor / Control Expert trainer, who's had a lot of experience with this type of programming. He stated that due to the nature of program units it's necessary to have this type of isolation for complete re-usability. If you're stuck on a specific issue, though, please feel free to reach out to our Global Customer Support team who have a lot of experience with these sorts of issues.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore