What are Status codes 1 and 2 in the MB_IP_MASTER / MB_SERIAL_MASTER functions?

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • What are Status codes 1 and 2 in the MB_IP_MASTER / MB_SERIAL_MASTER functions?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
75
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Solved
infinityscott
Crewman infinityscott
Crewman

Posted: ‎2025-03-24 06:36 AM

0 Likes
3
157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-24 06:36 AM

What are Status codes 1 and 2 in the MB_IP_MASTER / MB_SERIAL_MASTER functions?

I have a SCADAPack 474 which has been configured with polling as per the SE Community example. However, I have noticed that I am sometimes getting Status Code 1 or 2 - neither of these are listed in the Logic Editor help files.

 

What do these Status Codes relate to?

Labels
  • Labels:
  • RTU
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2025-03-27 07:58 AM . Last Modified: ‎2025-03-27 01:11 PM

In response to infinityscott
0 Likes
0
91
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-27 07:58 AM . Last Modified: ‎2025-03-27 01:11 PM

Hi again Scott,

 

My apologies for the incomplete response. I forgot to mention that you can get help even in Logic Editor for SCADAPack-specific function blocks. You won't find that help in the Logic Editor manual, as it's written & controlled by a different team. But there is always the "Help on Type" feature, as you've mentioned. Thanks for that reminder.

 

I've talked again with our RemoteConnect experts and they cannot understand how you might be seeing a status code 1 or 2. I've been told it's not that the documentation is incomplete, rather that those codes should simply never appear. As I mentioned in my previous message, they'd really like to get a copy of your application to analyze, see what's going on. That's the best path forward at this point.

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2025-03-25 07:49 AM

0 Likes
0
133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 07:49 AM

Hello Scott,

 

These function blocks are specific to the SCADAPack, they're not general Control Expert (Logic Editor) function blocks. So the help for them is in the RemoteConnect documentation, not the Logic Editor documentation. Here's how to find it:

- Open RemoteConnect, and select the Help (?) menu item

- Select the Logic Programming Manuals

- Open SCADAPack Function Blocks Technical Reference

- Open the Modbus Function Blocks section

- The two FB's in question are documented here

- In the Output parameter descriptions you'll find STATUS

- In the description a status of -1 indicates the request is in progress. (note it's a negative 1)

 

However, having written all that, the table of status codes does not include either 1 or 2. I can't tell you what those codes mean. I suggest you save your project as an RCZ archive file then send it to our Tech Support team so they can have a look.

 

SupportRO@se.com

or 1-888-226-6876

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

infinityscott
Crewman infinityscott
Crewman

Posted: ‎2025-03-26 02:09 AM

0 Likes
1
112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-26 02:09 AM

Hi Joel,

 

Sorry, but that's not really a helpful answer, and also incorrect. I am including the below for any who fces a similar issue in the future...

 

The Help file for these (and all built-in Logic Editor blocks) are available through Logic Editor as follows:-

 

Click Tools > Types Library Browser.

In the Types Library Browser window, in the Name box, enter the function name (* wildcard allowed), e.g. mb_ip* will return MB_IP_MASTER.

Right-click on the function in question and select Help On Type. A new window will open with the relevant Help HTML file loaded.
(These are actually HTMLs version of the relevant Remote Connect help file, but often more useful since they contain, in this example, the Status Codes embedded and not linked out to a separate pages.)

 

I did spot the -1 PENDING status and my graphics already cover that as a message; my point was that the Help literature (both in Remote Connect and Logic Editor) are missing Status Code information 1 and 2 that I know of. It then raises the question of what other codes may also be missing?

 

Ultimately, the help literature is incomplete and needs to be updated.

Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2025-03-27 07:58 AM . Last Modified: ‎2025-03-27 01:11 PM

In response to infinityscott
0 Likes
0
92
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-27 07:58 AM . Last Modified: ‎2025-03-27 01:11 PM

Hi again Scott,

 

My apologies for the incomplete response. I forgot to mention that you can get help even in Logic Editor for SCADAPack-specific function blocks. You won't find that help in the Logic Editor manual, as it's written & controlled by a different team. But there is always the "Help on Type" feature, as you've mentioned. Thanks for that reminder.

 

I've talked again with our RemoteConnect experts and they cannot understand how you might be seeing a status code 1 or 2. I've been told it's not that the documentation is incomplete, rather that those codes should simply never appear. As I mentioned in my previous message, they'd really like to get a copy of your application to analyze, see what's going on. That's the best path forward at this point.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now