SCADAPack 470i Edge application reflash

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • SCADAPack 470i Edge application reflash
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
SCADAPack™ 47x | 47xi

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
secres
Crewman secres
Crewman

Posted: ‎2025-02-17 01:46 AM

0 Likes
3
1224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 01:46 AM

SCADAPack 470i Edge application reflash

I have a SCADAPack 470i and I am using the Edge application for some testing. During the tests, I overwrote the linux dynamic linker file \lib\ld-32.so. This had the effect that all the dynamically compiled files where not able to execute including ls, cp and others. Eventually I lost connection with ssh and I was not able to recover one since SSH does use that file.

 

I attempted to do a firmware update from RemoteConnect but its fails with code 43. This is expected since the firmware update runs an internal command in the linux system, which actually cannot run because it uses the ld-32.so to do dynamically linking for executing the update, which eventually fails since the file is broken.

 

My question is, is there any way to recover the situation before sending the device back? The RTU is working and is able to do operations but the Edge part is completely non functioning. Is there an alternative way to reflash the firmware for the Edge part? Is there any interface that could work for me to get access to the device like serial just for the Edge part?

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2025-02-18 07:53 AM . Last Modified: ‎2025-02-18 07:56 AM

1 Like
1
1151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-18 07:53 AM . Last Modified: ‎2025-02-18 07:56 AM

Hello Secres,

 

The Edge firmware is typically loaded thru RemoteConnect. To be clear, in case you've not done it correctly, here's the procedure:

- Go online with the RTU (not the Edge board) using RemoteConnect

- Right-click on the SCADAPack x70 Controller Settings -DeviceDTM in My Network

- Select Additional Functions, then Update Device Firmware or Bootloader.

- The first option available is to update the Edge firmware.

- Insert a USB stick containing the firmware into USB port 2 or 3.

- Edge firmware file can be found in a sub-folder of the RemoteConnect install folder. Typically this is:
C:\ > Program Files (x86) > Schneider Electric > RemoteConnect > Firmware > Edge

 

If that procedure still does not work for you, I suggest you contact our Global Tech Support team, explaining in detail what's happened. Here's their contact info:

 

SupportRO@se.com   or

1-888-226-6876

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

secres
Crewman secres
Crewman

Posted: ‎2025-02-28 08:56 AM

In response to Joel_Weder
0 Likes
0
1053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-28 08:56 AM

Hi Joel,

 

Thanks for the hint. In the end the problem was resolved with a factory reset after an Edge SD card wiping. The first attempt to factory reset the device did not resolve the issue. After contacting SE support, seems like it was required to wipe out the SD card before the FR. After wiping the SD card of the Edge module and doing the FR process (button factory reset action + 90sec waiting), the Edge module was recovered. Seems like this was not expected as the Factory reset should wipe out the SD card.

 

Again thanks for the support

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-02-17 08:10 PM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 08:10 PM

I haven't actually played around with the SCADAPack47xi series.  During the initial discussion there was mention of being able to fully configure them just by using a USB dongle.

I don't know how far that actually got, but I would have expected USB firmware flash from bootloader would be in there (if nothing else).

Failing that, you could use the bootloader process to try to write in the firmware.  That shouldn't require any linux process to work.

I did give it a quick google, but unfortunately everything seems to point towards the 'pretty and fancy' RemoteConnect to do it.. without mentioning bootloader operation.  I'm pretty sure there was stuff in the user manual (at least from the SCADAPack 47x series) as to how to enter bootloader with a certain button push power cycle combo..


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2025-02-18 07:53 AM . Last Modified: ‎2025-02-18 07:56 AM

1 Like
1
1152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-18 07:53 AM . Last Modified: ‎2025-02-18 07:56 AM

Hello Secres,

 

The Edge firmware is typically loaded thru RemoteConnect. To be clear, in case you've not done it correctly, here's the procedure:

- Go online with the RTU (not the Edge board) using RemoteConnect

- Right-click on the SCADAPack x70 Controller Settings -DeviceDTM in My Network

- Select Additional Functions, then Update Device Firmware or Bootloader.

- The first option available is to update the Edge firmware.

- Insert a USB stick containing the firmware into USB port 2 or 3.

- Edge firmware file can be found in a sub-folder of the RemoteConnect install folder. Typically this is:
C:\ > Program Files (x86) > Schneider Electric > RemoteConnect > Firmware > Edge

 

If that procedure still does not work for you, I suggest you contact our Global Tech Support team, explaining in detail what's happened. Here's their contact info:

 

SupportRO@se.com   or

1-888-226-6876

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

secres
Crewman secres
Crewman

Posted: ‎2025-02-28 08:56 AM

In response to Joel_Weder
0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-28 08:56 AM

Hi Joel,

 

Thanks for the hint. In the end the problem was resolved with a factory reset after an Edge SD card wiping. The first attempt to factory reset the device did not resolve the issue. After contacting SE support, seems like it was required to wipe out the SD card before the FR. After wiping the SD card of the Edge module and doing the FR process (button factory reset action + 90sec waiting), the Edge module was recovered. Seems like this was not expected as the Factory reset should wipe out the SD card.

 

Again thanks for the support

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore