Trio QR450 NTP Server

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • Trio QR450 NTP Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
HD90
Crewman HD90
Crewman

Posted: ‎2022-07-03 06:16 PM

0 Likes
4
2314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-03 06:16 PM

Trio QR450 NTP Server

Hi all,

 

I'm trying to setup a network with six QR450. To simplify the question, let's consider only 2.

 

I want both radios to act as NTP server and client. So, I have enabled both options. The first radio is connected to my laptop (via Ethernet) which is running an NTP server. It successfully syncs time as a client. 

 

For the second radio, I want it to sync its time with the first radio. They are talking over radio not Ethernet.  So, I enter the WAN IP address of the first radio as the NTP server. However, it doesn't sync as a client.

 

Am I missing anything? I couldn't find any other config.

Labels
  • Labels:
  • Radio
  • Tags:
  • english
  • ntp
  • QR450
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
  • Trio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-07-03 08:58 PM

1 Like
3
2295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-03 08:58 PM

I suspect that the NTP Server won't respond to NTP requests on its Radio (WAN) interface as default, since that would generally be a bit insecure.

You should use the LAN IP address, or (NOT RECOMMENDED) change the firewall rules to allow for NTP Server traffic on the Radio interface. 

 

2022-07-04 13_57_57-Window.png


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

HD90
Crewman HD90
Crewman

Posted: ‎2022-07-03 09:49 PM

In response to BevanWeiss
0 Likes
2
2283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-03 09:49 PM

Thanks for the answer and your time Bevan.

 

For these two radios, it's not possible to use the LAN IP. I had already allowed Radio in the firewall for NTP. But, still not working. 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-07-04 04:08 AM

In response to HD90
0 Likes
1
2271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-04 04:08 AM

Have you confirmed that the NTP Client can indeed communicate with the NTP Server on the WAN port?

i.e. via PING or similar from the NTP Client device

 

You'll probably need to provide your testbench configuration screenshots, showing both the NTP client and the NTP server's NTP (and IP) configurations.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2022-07-04 08:13 AM . Last Modified: ‎2022-07-04 08:15 AM

In response to BevanWeiss
1 Like
0
2262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-04 08:13 AM . Last Modified: ‎2022-07-04 08:15 AM

A couple of related comments:

 

1) Typically only ONE radio on the wireless network will be configured as NTP Server. You stated that BOTH of your radios are configured as BOTH Server and Client. I see no need for that.

 

2) If there is a reliable and secure connection to an external NTP server, then typically ONE radio (usually the master site radio, connected to the gateway) will be configured as both an NTP Client (to get time from the external server) and as an NTP Server, to provide the time to other radios on the system. In this case, all other radios on the network will be configured with the entry point radio's IP address as their NTP server.

 

3) If there is no secure (cyber-protected) network connection to an external NTP Server, the Entry Point radio (configured as the NTP Server) may be manually configured on occasion with the correct time and date. All other radios on the network (configured as Clients) will then sync to it.

 

P.S. Remember that the ONLY use for time/date in a Trio radio is to provide time stamping in the Alarm and Event Log.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore