SCADAPack 47x firmware update using GeoSCADA

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • SCADAPack 47x firmware update using GeoSCADA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
SCADAPack 47x

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
Tyrone19
Lieutenant Tyrone19 Lieutenant
Lieutenant

Posted: ‎2022-05-29 04:11 AM

0 Likes
3
2271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-29 04:11 AM

SCADAPack 47x firmware update using GeoSCADA

Hi Community

 

I am currently trying to update the firmware of my SCADAPack using GeoSCADA however having issues with this. I have also tried with the 57x but get the same problem. The request always times out as seen in attachments. Anyone know what could cause this and how i could solve it. I have the scadapack directly connected to my PC just to rule out any coms issues.

 

Thank you!

Attachments
Labels
  • Labels:
  • SCADA
  • Telemetry
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-05-29 09:03 PM

0 Likes
2
2244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-29 09:03 PM

What are your current versions of Bootloader and Firmware, and which version of Bootloader / Firmware are you going to?

 

I would generally recommend using RemoteConnect to do the first firmware version upgrade (from base to new) just to make sure that the process will actually work without problem.

 

The GeoSCADA Expert process is pretty basic, and it doesn't provide much indication of errors.

It really just does a DNP3 file transfer, and then a reboot firmware upgrade command.

If anything goes wrong in that, GeoSCADA Expert wouldn't know.  But RemoteConnect would have a better idea.

 

It's possible you're trying to upgrade to a firmware version that doesn't match your bootloader version, and hence it's refusing to upgrade.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Tyrone19
Lieutenant Tyrone19 Lieutenant
Lieutenant

Posted: ‎2022-06-27 12:31 AM

In response to BevanWeiss
0 Likes
1
2126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-27 12:31 AM

Hi Bevan, I did try through Remote connect and it worked perfectly.

 

I then tried again through GeoSCADA and it did not work. But bare in mind that the versions would be the same now. I'm assuming that if the versions are the same then it would not be able to update - Am I correct about this?

 

Are there any ways on GeoSCADA directly to see any error code.

 

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-06-27 08:28 PM

In response to Tyrone19
0 Likes
0
2098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-27 08:28 PM

GeoSCADA Expert is restricted by the DNP3 protocol around this.. so there's very little diagnostic information available on this.

That's why it's generally better to do the first couple of firmware upgrades via RemoteConnect, and then confirm on a bench test that the firmware upgrade will work through GeoSCADA Expert.

 

That's correct that if the version is the same it wouldn't like that.  Many new firmware versions can't be downgraded either (for secuity reasons generally..), so that would cause a failure, but without much in the way of diagnostics.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore