Serck Enet RTU software
Hello,
I am looking into how to connect and program an old Serck Enet 2006 Controller.
I tried to find the software but could not find it.
Would it be possible to know what software I would need to connect to the controller and where I will be able to find them please?
- Labels:
-
RTU
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-16 05:07 AM
Thanks Bevan, I was able to connect to the RTU using the latest Eserise configurator 8.18.1
I had to make a custom cable as shown in the manual. It was a custom DB9 to RJ11 3 wire connection.
I connect it to port 4 (Diagnostic port) and as per the manual typed "WHOAMI" and it spit out all the other port config parameters.
There on it was easy to connect to the ethernet port.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 08:42 PM
I'm not familiar with the eNET 2006.
But if you can work out if this is a 386 or a 586 that will start to get you closer to working out which firmware / software might work for it.
In general both the 386 and 586 eNETs used the E Series Configurator and E Series Firmware (hence will work with either ISaGRAF for E Series, or SCADAPack Workbench for E Series).
Depending on what firmware version you can get into them will limit what functions and what version of the E Series Configurator software you can use.
If the eNET 2006 is neither 386 nor 586, then you might be stuck..
Your local Schneider tech support can probably provide some additional help, they likely have some documentation from the Serck days.
Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-16 05:07 AM
Thanks Bevan, I was able to connect to the RTU using the latest Eserise configurator 8.18.1
I had to make a custom cable as shown in the manual. It was a custom DB9 to RJ11 3 wire connection.
I connect it to port 4 (Diagnostic port) and as per the manual typed "WHOAMI" and it spit out all the other port config parameters.
There on it was easy to connect to the ethernet port.