Posted: 2022-04-10 12:13 AM
Scadapack RS485 comm issues
I am having issues communicating to a valve on an RS485 network. There are a total of 10 valves and the RS485 is daisy chained starting from the PLC to the first valve, and onwards to the last valve. The issue is I can see all of the valves utilizing modscan, except the first one the PLC is daisy chained to. I am not sure if there are termination resistors wired. Is there any reason I cannot see the first valve in the daisy chain but all others?
- Labels:
-
SCADA
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-04-11 10:37 AM
Hi Kevin,
Attached is an old document I sometimes refer to when dealing with an RS-485 issue. Please dig into that and check all the various issues discussed. One other item to consider is "What's different about that first valve?" Maybe different firmware, maybe a different switch setting, maybe a poor terminal connection, could be any of many different things...
Joel
Remote Operations Specialist
Schneider Electric
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-04-11 10:37 AM
Hi Kevin,
Attached is an old document I sometimes refer to when dealing with an RS-485 issue. Please dig into that and check all the various issues discussed. One other item to consider is "What's different about that first valve?" Maybe different firmware, maybe a different switch setting, maybe a poor terminal connection, could be any of many different things...
Joel
Remote Operations Specialist
Schneider Electric
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-23 06:54 PM
i used to get same issue as well.