Hello
Does someone know how could we read the workbench file (*.isasln) from a RTU SCADAPack 333 E if we don't have the file available on our PC?
I could write *.I5P file to RTU. I create a new project in the Workbench app and set IP address as RTU has been set. Upload button is disabled in workbench and when I tried to read file from E-Configurator I got this error message
"Request: File Read Request. DNP Status: Unsuccessful".
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-23 01:52 PM
Hello AliG,
Regrettably your post was in the Geo SCADA forum so we missed it until now. The only way to retrieve the logic application from a SCADAPack E type RTU is to perform an FTP file transfer of the compiled code. That file could then be transferred into an identical RTU, again via FTP. However, if your goal is to then modify the application in Workbench that is not possible. The compiled file unfortunately cannot be "de-compiled".
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-23 01:52 PM
Hello AliG,
Regrettably your post was in the Geo SCADA forum so we missed it until now. The only way to retrieve the logic application from a SCADAPack E type RTU is to perform an FTP file transfer of the compiled code. That file could then be transferred into an identical RTU, again via FTP. However, if your goal is to then modify the application in Workbench that is not possible. The compiled file unfortunately cannot be "de-compiled".
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-23 03:48 PM
Hi Joel,
Thank you for your reply.
Regards,
Ali