SCADAPack 5407 replacement

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • SCADAPack 5407 replacement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
Abanoub
Ensign Abanoub Ensign
Ensign

Posted: ‎2021-12-20 08:20 AM . Last Modified: ‎2021-12-20 08:21 AM

0 Likes
7
3138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-20 08:20 AM . Last Modified: ‎2021-12-20 08:21 AM

SCADAPack 5407 replacement

Hi community,

 

I am searching for a direct replacement for SCADAPack DO Expansion module 5407.

 

Here are the specs of 5407 we have to comply..

Operate time = 5ms typical 10ms max

Release time = 2ms typical 10ms max

Bounce Time = 3ms typical

 

Max current/ channel = 2A.

 

Appreciate your support.

Labels
  • Labels:
  • RTU
  • Tags:
  • 5407
  • digital output
  • SCADAPack
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2021-12-20 09:12 AM

1 Like
3
3129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-20 09:12 AM

The most similar replacement module for the 5407 8-point relay output module is the 5415, which is a 12-point relay output module. However, the 5415 does not match the specifications you have listed, with 20ms typical Operate time and 25ms typical Release time.

 

For very fast Operate and Release time you may want to consider a solid-state (FET) output module rather than a relay module. They switch so quickly that these specs are not even noted. The 5409 can handle 2 amps continuous on each output, for example.  You did not mention the voltage being switched - the 5409 is typically for 12 or 24 volt systems.

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-12-21 02:16 PM

In response to Joel_Weder
1 Like
2
3120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-21 02:16 PM

Important to note that FET outputs can only handle DC voltages/currents.  Which is generally the most common anyway.

 

However, it's still not uncommon to see 12VAC / 24VAC field actuators in use, which would require either a dry contact relay style output, or an alternative solid state relay (thyristor driven, not FET).

 

My suggestion would be to utilise the 5409 with a 24VDC supply, and then if AC switching is required (or anything else requiring true dry contacts) to utilise some slimline terminal relays (these are available from a large number of vendors, ABB, Finder, Phoenix Contact, Allen-Bradley, etc, etc.. heck probably even Schneider).

 

The Finder 38 series relays are in the <10ms range for the electromechanical type, the SSR type are generally sub-ms

https://www.finder-relais.net/en/finder-relays-series-38.pdf


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

MartinChartrand
Captain MartinChartrand Captain
Captain

Posted: ‎2021-12-22 05:09 AM

In response to Abanoub
1 Like
0
3098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-22 05:09 AM

Just a minor correction to the conversation, the 5409 is still available and can be ordered using part number TBUX297117. It was not on the list of 5000-Series I/O expansion modules that were retired in 2020 or 2021.

 

Martin

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

MartinChartrand
Captain MartinChartrand Captain
Captain

Posted: ‎2021-12-23 06:08 AM

In response to Abanoub
0 Likes
0
3081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-23 06:08 AM

Hello,

I can't get you name of the components easily but I can provide the specifications from the user manuals.

 

Please note that the 5415 comes in two versions: Dry Contact and Solid State relays. I have included their specs here as well as for the obsolete 5407.

 

5415 Dry Contact Relay Version
Contact rating:

  • 3 A, 30 Vdc or 250 Vac (Resistive)
  • 1000 Vac between open contacts
  • 12 A maximum per common

Switching Capacity:

  • 5 A, 30 Vdc (150 W Resistive)
  • 5 A X 250 Vac (1250 VA Resistive)

Service Life:

  • 2 X 107 mechanical
  • 1 X 105 at 5 A, 30 Vdc or 250 Vac

Bounce Time: 1 ms typical


5415 DC Solid State Relay Version
Load voltage: 60 Vdc maximum
Load current:

  • 3 A continuous maximum at 50ºC (122ºF) ambient
  • 2 A continuous maximum at 70ºC (158ºF) ambient
  • 9 A peak, 100ms
  • UL508 rated 2 A at 50 ºC and 1.33A at 70 ºC (158 ºF.)

On resistance: 0.09 ohms
Off state leakage current: 10 uA
Service Life: Unlimited
Bounce Time: None

 

 

 

5407
Type

  • Sealed mechanical relay
  • Form A (normally open) contacts.
  • Can be modified for Form B (normally closed) contacts.

Contact Ratings:

  • 6 A at 250 VAC resistive loads
  • 6 A at 30 VDC resistive loads
  • 3 A maximum in Class 1, Div, 2 hazardous locations.

Operating Frequency: 18,000 operations/hour mechanically, 1,800 electrically at rated load
Service Life:

  • 1,500,000 operations at 0...250 mA load
  • 600,000 operations at 1 A resistive load
  • 100,000 operations at 6 A resistive load
  • 300,000 operations at 1 A inductive loads with pf =0.4
  • 100,000 operations at 3.5 A inductive loads with pf=0.4

Operate Time: 10 ms maximum, 5 ms typical
Release Time: 10 ms maximum, 2 ms typical
Bounce Time: 3 ms typical
Contact Isolation: 1000 VAC
Logic Isolation: 1500 VAC

 

Regards,

Martin

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2021-12-20 09:12 AM

1 Like
3
3130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-20 09:12 AM

The most similar replacement module for the 5407 8-point relay output module is the 5415, which is a 12-point relay output module. However, the 5415 does not match the specifications you have listed, with 20ms typical Operate time and 25ms typical Release time.

 

For very fast Operate and Release time you may want to consider a solid-state (FET) output module rather than a relay module. They switch so quickly that these specs are not even noted. The 5409 can handle 2 amps continuous on each output, for example.  You did not mention the voltage being switched - the 5409 is typically for 12 or 24 volt systems.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-12-21 02:16 PM

In response to Joel_Weder
1 Like
2
3121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-21 02:16 PM

Important to note that FET outputs can only handle DC voltages/currents.  Which is generally the most common anyway.

 

However, it's still not uncommon to see 12VAC / 24VAC field actuators in use, which would require either a dry contact relay style output, or an alternative solid state relay (thyristor driven, not FET).

 

My suggestion would be to utilise the 5409 with a 24VDC supply, and then if AC switching is required (or anything else requiring true dry contacts) to utilise some slimline terminal relays (these are available from a large number of vendors, ABB, Finder, Phoenix Contact, Allen-Bradley, etc, etc.. heck probably even Schneider).

 

The Finder 38 series relays are in the <10ms range for the electromechanical type, the SSR type are generally sub-ms

https://www.finder-relais.net/en/finder-relays-series-38.pdf


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Abanoub
Ensign Abanoub Ensign
Ensign

Posted: ‎2021-12-21 11:23 PM

In response to BevanWeiss
0 Likes
1
3110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-21 11:23 PM

@Joel_Weder, @BevanWeiss Thanks for your concern!

 

The problem is that 5409 doesn't exist on BuyAutomation and i think it is obsolete so do 5407.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

MartinChartrand
Captain MartinChartrand Captain
Captain

Posted: ‎2021-12-22 05:09 AM

In response to Abanoub
1 Like
0
3099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-22 05:09 AM

Just a minor correction to the conversation, the 5409 is still available and can be ordered using part number TBUX297117. It was not on the list of 5000-Series I/O expansion modules that were retired in 2020 or 2021.

 

Martin

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Abanoub
Ensign Abanoub Ensign
Ensign

Posted: ‎2021-12-23 01:38 AM

0 Likes
2
3087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-23 01:38 AM

Pretty clear, Thanks all!

 

However, we received a clarification from the customer asking to know the internal built-in relays type in module 5415 compared with the old type Omron relays in the obsolete module 5407.

Can we get this data?

 

@Joel_Weder, @BevanWeiss, @MartinChartrand 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

MartinChartrand
Captain MartinChartrand Captain
Captain

Posted: ‎2021-12-23 06:08 AM

In response to Abanoub
0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-23 06:08 AM

Hello,

I can't get you name of the components easily but I can provide the specifications from the user manuals.

 

Please note that the 5415 comes in two versions: Dry Contact and Solid State relays. I have included their specs here as well as for the obsolete 5407.

 

5415 Dry Contact Relay Version
Contact rating:

  • 3 A, 30 Vdc or 250 Vac (Resistive)
  • 1000 Vac between open contacts
  • 12 A maximum per common

Switching Capacity:

  • 5 A, 30 Vdc (150 W Resistive)
  • 5 A X 250 Vac (1250 VA Resistive)

Service Life:

  • 2 X 107 mechanical
  • 1 X 105 at 5 A, 30 Vdc or 250 Vac

Bounce Time: 1 ms typical


5415 DC Solid State Relay Version
Load voltage: 60 Vdc maximum
Load current:

  • 3 A continuous maximum at 50ºC (122ºF) ambient
  • 2 A continuous maximum at 70ºC (158ºF) ambient
  • 9 A peak, 100ms
  • UL508 rated 2 A at 50 ºC and 1.33A at 70 ºC (158 ºF.)

On resistance: 0.09 ohms
Off state leakage current: 10 uA
Service Life: Unlimited
Bounce Time: None

 

 

 

5407
Type

  • Sealed mechanical relay
  • Form A (normally open) contacts.
  • Can be modified for Form B (normally closed) contacts.

Contact Ratings:

  • 6 A at 250 VAC resistive loads
  • 6 A at 30 VDC resistive loads
  • 3 A maximum in Class 1, Div, 2 hazardous locations.

Operating Frequency: 18,000 operations/hour mechanically, 1,800 electrically at rated load
Service Life:

  • 1,500,000 operations at 0...250 mA load
  • 600,000 operations at 1 A resistive load
  • 100,000 operations at 6 A resistive load
  • 300,000 operations at 1 A inductive loads with pf =0.4
  • 100,000 operations at 3.5 A inductive loads with pf=0.4

Operate Time: 10 ms maximum, 5 ms typical
Release Time: 10 ms maximum, 2 ms typical
Bounce Time: 3 ms typical
Contact Isolation: 1000 VAC
Logic Isolation: 1500 VAC

 

Regards,

Martin

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-12-23 05:20 PM

In response to Abanoub
0 Likes
0
3075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-23 05:20 PM

The internal part numbers would not be guaranteed for either the old or the new IO modules.

These may vary from time to time, hence only the final product specifications would be guaranteed.

 

You'd likely find that the 5415 relays will have a faster response than listed, and may indeed be identical internal relays to the 5407.  But you shouldn't rely on this information, and Schneider could change the relays used in the 5415 with some that work slower (as long as they are still within the published specifications).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore