PIDD Telepace

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • PIDD Telepace
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
76
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
willB1
Crewman willB1
Crewman

Posted: ‎2020-07-28 07:27 AM

0 Likes
7
3496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-28 07:27 AM

PIDD Telepace

Trying to develop an easy way to run a vent from fully open to fully closed and all positions in between using a PIDD block. The opening/closing is done to maintain a temperature in a room (set point 75F). Fully closed-open takes 60 seconds. Iv'e set the full and zero at -50 and +50. Each output controls independent relays (1 open and 1 close). Is there a way to use PIDD for this purpose?  I'm obviously missing something because i can't get it to work like i want it.

Labels
  • Labels:
  • Logic
  • SCADA
  • Telemetry
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2020-07-28 07:47 AM . Last Modified: ‎2020-07-28 07:48 AM

0 Likes
2
3494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-28 07:47 AM . Last Modified: ‎2020-07-28 07:48 AM

Hello WillB1,

 

This should certainly be possible to manage with PIDD. You'll need a temperature input to the RTU as your Process Value, and two digital outputs. One will pulse to increase temperature, and the other will pulse to decrease temperature. That's probably the most challenging part of this, getting those digital outputs properly wired to your vent control motor. We can't really help you much with that, as it's so specific to your application.

 

Not knowing whether you've taken a Telepace course or not, I can certainly recommend you sign up for one if not, and if there's one available in your area. However, I'm attaching a few pages from the training manual, covering the PIDA exercise. Unfortunately there's no PIDD exercise, but they operate in a generally similar way. The Help documentation for PIDD is pretty good, though.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Attachments
  • Tags:
  • english
  • Telepace
Reply

Link copied. Please paste this link to share this article on your social media post.

willB1
Crewman willB1
Crewman

Posted: ‎2020-07-28 08:14 AM

In response to Joel_Weder
0 Likes
1
3490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-28 08:14 AM

Thanks for the fast response. I have the input temperature coming into the PIDD and the outputs wired correctly. I guess the issue is understanding the cycle time vs other tuning inputs to allow the vents to open/close a certain distance (time)/ distance the temp is away from set point 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2020-07-28 10:13 AM

In response to willB1
0 Likes
0
3485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-28 10:13 AM

@willB1,

 

Probably the most challenging aspect of PID control is tuning of the parameters. The exercise I attached does include some pointers about initial settings of the Proportional and Integral parameters. (Derivative is rarely used in cases such as this) Also, any scaling in logic can dramatically impact the results if done incorrectly. 

 

If after working through the exercise and Help documentation for PIDD you're still having issues, please feel free to contact our Tech Support team. They'll want to see a copy of your logic as well as a drawing of the wiring you've implemented.

 

SupportTRSS@se.com  or

1-888-226-6876

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-07-28 05:35 PM

0 Likes
3
3479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-28 05:35 PM

Are you able to break the problem into two parts (i.e. do you have any positional feedback from the vent?)?

 

If you were in the RemoteConnect / Unity world, then there is a SERVO function block that would allow for the Vent position control, and then it should be a relatively straight forward approach to wrap the commanded position with a PIDFF to perform the Temperature -> Vent position control.

 

Or as Joel suggested, you could tailor the scale to a timeduration, and every X seconds (or minutes) trigger the valve movement for Y seconds (based upon the value of the control output from the PIDD).

 

I'm not familiar with the Telepace platform, but sometimes there is already a split range controller.  There's nothing like that there?


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

willB1
Crewman willB1
Crewman

Posted: ‎2020-08-03 07:23 AM

In response to BevanWeiss
0 Likes
2
3438
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-03 07:23 AM

Thanks for the help. I have not configured a PIDD. So here is the issue. The total open-close time is approximately 60 seconds. I'm having trouble with the min/max where the pulse output isn't consistent. Like you, I'd like to have it open/close for say 10 seconds to increase or decrease temperature. Thanks again. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PLCs_4_Me
Ensign PLCs_4_Me
Ensign

Posted: ‎2022-01-02 01:25 PM

In response to willB1
0 Likes
1
1806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-02 01:25 PM

We use PIDA to control the water level at our pump station at 45 inches via VFD. We use the SCAL function element with a pressure transducer with 4-20mA signal to set the process value we need (45 inches 4mA=0 20mA=415 inches 15 PSI transducer). In your situation it sounds like you need a RTD temperature sensor (measurement range 0-200 degrees F) with a 4-20mA output signal and connect that to your PLC analog input. SCAL the analog input with the RTD. Once that is done, you can set up your PIDD Block to input all the necessary info.  Your set point is 75. Your Gain, reset time, rate time and deadband. Full (%) I assume would be +30 and Zero (%) would be -30 ( for a total of 60 seconds which is the total time to close.) Then you just have the logic compare the set point to the actual temperature reading and create two blocks to control the digital outputs to either open the valve or close it depending on the values (actual temp=100 F > 75 F setpoint open the valve) etc. Let me know if this helps.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-01-03 04:28 PM

In response to PLCs_4_Me
0 Likes
0
1800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-03 04:28 PM

PIDA is generally to control an analog output, and it expects that its output is acted on each cycle.

This is different than a PIDD where the output is a digital output that will be integrated over time to get the control response.

 

The front part is the same however, so there does need to be an analog input for the temperature, to be compared against the setpoint temperature.

 

The total time to open/close is only really relevant as it pertains to the gain of the system.  The biggest impact is likely to be the system response to actuator position however.  So when the vent is opened, how long it takes for a temperature change to be detected.

This is where the 'loop tuning' starts to factor in.  With a long system response time, then the system gain should be reduced, otherwise you will end up with overshoot (and likely response oscillation).  I would suggest starting with a very low gain, and working upwards from there.  Likewise, having a low Full % value is likely a good start.  Perhaps as low as 10% (6 seconds of valve movement in each minute).  The cycle time will also relate back to the system response time lag.  No point having the PIDD executing frequently and 'winding up' its response if the previous output change hasn't had any time to propagate yet.

 

It's also important to remember that a PID expects a somewhat linear characteristic of system response.  This often isn't true, especially when valves are involved.  It may be desirable to perform some linearisation process.  Unsure how that would be done without position feedback on the valve itself... but all of these things become factors in the control system.

 

For reference, I would consider the best case control to be what I mentioned originally.  Split the system into two loops.

The first controls for temperature against a valve position.  The second controls valve position (based on valve potentiometer feedback or similar) and runs a motor to open/close valve.  This is generally how things like air conditioning systems with variable dampers work.  It really makes the whole control easier.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of