SCADAPack 330E won't communicate with Configurator "IIN bits set"

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • SCADAPack 330E won't communicate with Configurator "IIN bits set"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
AndrewG
Crewman AndrewG
Crewman

Posted: ‎2023-01-13 04:37 PM

0 Likes
4
2678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-13 04:37 PM

SCADAPack 330E won't communicate with Configurator "IIN bits set"

Hi People,

I have a 330E that has been sitting on a shelf for a few years (previously working), and have recently re-installed SCADAPack E Configurator (and Workbench) to a new windows 10 laptop.

When trying a USB connection (Refresh button from Controller Status page), I'm getting a modal dialog box error :

"Request: Page Read Request"

"Status: DNP Status: Function code not supported (IIN bits set)

The configuration diagnostics then have a few messages (pasted below).

I've tried Cold Boot Mode and Factory Boot Mode without any improvement.  Any ideas?

 

<+++ Master 32000 Build DNP3 Message: Table Read

<+++ Master 32000 Insert request in queue: Table Read

<=== Master 32000 Application Header, Read Request
FIR(1) FIN(1) CON(0) UNS(0) SEQ# 4

===> Master 32000 Application Header, Response
FIR(1) FIN(1) CON(0) UNS(0) SEQ# 4

+++> Master 32000 Process response to request: Table Read

===> Master 32000 IIN Bits:
IIN1.6 Device Trouble
IIN2.5 Configuration Corrupt
IIN2.0 Function Code Not Implemented

Labels
  • Labels:
  • DNP3
  • RTU
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewG
Crewman AndrewG
Crewman

Posted: ‎2023-01-19 04:56 PM

0 Likes
0
2603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-19 04:56 PM

The issue was resolved by a more recent SCADAPack E Configurator (the download / configuration software) supplied by Schneider.


It appears the SCADAPack Firmware was too new for the older loader software.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2023-01-16 09:06 AM . Last Modified: ‎2023-01-16 09:26 AM

0 Likes
0
2649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-16 09:06 AM . Last Modified: ‎2023-01-16 09:26 AM

Hi Andrew,

 

You may want to start with a factory boot. The procedure is described in the SCADAPack 330 Reference Manual (available from SCADAPack E Configurator "Help"), but the process is simple. 

- Remove power from the RTU

- Press and hold the white button

- Apply power to the RTU

- Keep holding the button and watch the STAT LED. It'll start flashing, then stop again. After it is on continuously, let go of the button.

- Wait a minute for the RTU to reboot


If a factory boot doesn't work, you may want to contact our Australian support team for faster assistance. Here's a link to the support contact page, which includes both a form you can fill out, and below that a contact phone number. Make sure you tell them the version of SCADAPack E Configurator and the exact SCADAPack model. They may ask for the firmware version, but as you can't communicate with the RTU you may not be able to provide that.

https://www.se.com/au/en/work/support/customer-care/contact-schneider-electric.jsp

 

NOTE: After some years of sitting idle, the RTU's RAM backup battery may be weak or dead. We suggest you purchase a replacement through normal channels and replace the battery. Part number is TBUM297592 or if you have local supply, any of these will work:

Tadiran TL-5186, OmniCel ER22G68 or Eve Energy ER22G68

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • rtu
  • SCADAPack
Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2023-01-17 08:57 AM

0 Likes
0
2637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-17 08:57 AM

P.S. If by chance you're NOT in Australia (seems your company's head office may be there) perhaps you're in North America. In any case here's how you can find appropriate Support assistance:

 

- Open a web browser and go to se.com

- Open the Support menu and select Contact Support

- Select your region of the world e.g. North America

- Then select your specific country or sub-region

- Scroll down and depending on region you'll be presented with a contact form or phone number to call

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewG
Crewman AndrewG
Crewman

Posted: ‎2023-01-17 09:57 AM

0 Likes
0
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-17 09:57 AM

Understood.  I have posted to the USA support area, tried another couple of factory boots, and have a battery on order.

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewG
Crewman AndrewG
Crewman

Posted: ‎2023-01-19 04:56 PM

0 Likes
0
2604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-19 04:56 PM

The issue was resolved by a more recent SCADAPack E Configurator (the download / configuration software) supplied by Schneider.


It appears the SCADAPack Firmware was too new for the older loader software.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore