SCADAPack 32 Analog Input reading high

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • SCADAPack 32 Analog Input reading high
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
75
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Syrio
Crewman Syrio
Crewman

Posted: ‎2021-09-13 01:15 PM

0 Likes
2
1415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-13 01:15 PM

SCADAPack 32 Analog Input reading high

I have a SCADAPack 32 w/ FW version 2.23 and I am having an issue with one of the analog inputs reading slightly high. 

 

When the analog input signal is ~4mA my raw counts are ~6700 when it should be closer to 6553. If I move the input to another channel it reads ~6553. I have tried putting a different analog input to this "bad" channel and it reads high as well. Is it just a bad channel or is there something causing this one input to read high? 

 

 

Labels
  • Labels:
  • RTU
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2021-09-14 11:46 AM

0 Likes
1
1400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-14 11:46 AM

Hello Syrio,

 

I'm not sure what the issue might be, but here are a few possibilities:

- Component out of calibration - would require repair or replacement of the board. Most likely candidate would be the 250 ohm current-sensing resistor for the faulty channel.

- The current/voltage selector jumper might be in the wrong position. Read the 5601 board's hardware manual for details. (p 19-20)

- Also check the DIP switches for 0-20 or 4-20 mA input selection. Probably not the issue but worth a look.

 

If you're not able to solve this issue, please do reach out to our Tech Support team who may have more suggestions.

 

SupportTRSS@se.com   or...

1-888-226-6876

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Syrio
Crewman Syrio
Crewman

Posted: ‎2021-09-14 03:05 PM

In response to Joel_Weder
0 Likes
0
1397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-14 03:05 PM

I verified the current/voltage selector jumper on the 5601A board and they are all set to mA. I also verified the DIP switch setting for 0-20mA or 4-20mA and it is at the 0-20mA setting. Otherwise, when putting in 4mA my raw counts would be 0 with the 20% offset. I feel like your first comment relating to the calibration and the 250 Ohm resistor is the most likely issue. I will try your customer support line. I have had this issue on more than one SCADAPack 32 unit. 

 

Thank you for your response.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now