I have a SCADAPack 32 w/ FW version 2.23 and I am having an issue with one of the analog inputs reading slightly high.
When the analog input signal is ~4mA my raw counts are ~6700 when it should be closer to 6553. If I move the input to another channel it reads ~6553. I have tried putting a different analog input to this "bad" channel and it reads high as well. Is it just a bad channel or is there something causing this one input to read high?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-14 11:46 AM
Hello Syrio,
I'm not sure what the issue might be, but here are a few possibilities:
- Component out of calibration - would require repair or replacement of the board. Most likely candidate would be the 250 ohm current-sensing resistor for the faulty channel.
- The current/voltage selector jumper might be in the wrong position. Read the 5601 board's hardware manual for details. (p 19-20)
- Also check the DIP switches for 0-20 or 4-20 mA input selection. Probably not the issue but worth a look.
If you're not able to solve this issue, please do reach out to our Tech Support team who may have more suggestions.
SupportTRSS@se.com or...
1-888-226-6876
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-14 03:05 PM
I verified the current/voltage selector jumper on the 5601A board and they are all set to mA. I also verified the DIP switch setting for 0-20mA or 4-20mA and it is at the 0-20mA setting. Otherwise, when putting in 4mA my raw counts would be 0 with the 20% offset. I feel like your first comment relating to the calibration and the 250 Ohm resistor is the most likely issue. I will try your customer support line. I have had this issue on more than one SCADAPack 32 unit.
Thank you for your response.