RemoteConnect Oject Database / Logic Editor inconsistencies mus be resolved before writing to the SCADAPack x70

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • RemoteConnect Oject Database / Logic Editor inconsistencies mus be resolved before writing to the SCADAPack x70
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
AlbertoArdila
Lieutenant AlbertoArdila
Lieutenant

Posted: ‎2022-05-25 12:19 PM . Last Modified: ‎2022-05-25 12:19 PM

0 Likes
5
3996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-25 12:19 PM . Last Modified: ‎2022-05-25 12:19 PM

RemoteConnect Oject Database / Logic Editor inconsistencies mus be resolved before writing to the SCADAPack x70

Hi,

 

I have the message: “Object Database / Logic Editor inconsistencies must be resolved before writing to the SCADAPack” when I try to write my program from RemoteConnect to a RTU 474.


When I build the program, the Process succeeded: 0 Error(s), 0 Warning(s)


I don’t see any error in the Object browser.


Is there someone that can tell me how I can solve this problem?

 

Thank you

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AlbertoArdila
Lieutenant AlbertoArdila
Lieutenant

Posted: ‎2022-06-08 05:20 AM

In response to BevanWeiss
1 Like
1
3885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-08 05:20 AM

Hi BevanWeiss.  Thanks for the answer

 

This error was that I created some objects in RemoteConnect and after those objects was loss but SCADAPack X70 Logic was unable to detect those missing object whit the Rebuild.

 

I tried update & Build Logit, Unlock Variable and Replace Variables but didn’t work.

 

My solution:

 

I exported the configuration from RemoteConnect, additional functions, export to Excel File, and then imported it from Excel to RemoteConnect, additional functions, Import from Excel File. After that, SCADAPack x70 Logic showed me lost objects.

At the end I needed to write all the Objects lost (+- 20).

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-05-25 09:14 PM

0 Likes
4
3977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-25 09:14 PM

My recollection is that there is something under the Advanced options in RemoteConnect to essentially force a resynchronisation of the Object Database with the Logic Editor.

You definitely want to have a backup of your project before doing this of course, since otherwise it could break everything..

 

I haven't seen your exact issue before however, but I have seen mismatches that had to be resolved through the full push from Object Database -> Logic Editor.  and these generally did break some of hte Logic Editor linkages (since variables did get deleted / renamed outside)


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

AlbertoArdila
Lieutenant AlbertoArdila
Lieutenant

Posted: ‎2022-06-08 05:20 AM

In response to BevanWeiss
1 Like
1
3886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-08 05:20 AM

Hi BevanWeiss.  Thanks for the answer

 

This error was that I created some objects in RemoteConnect and after those objects was loss but SCADAPack X70 Logic was unable to detect those missing object whit the Rebuild.

 

I tried update & Build Logit, Unlock Variable and Replace Variables but didn’t work.

 

My solution:

 

I exported the configuration from RemoteConnect, additional functions, export to Excel File, and then imported it from Excel to RemoteConnect, additional functions, Import from Excel File. After that, SCADAPack x70 Logic showed me lost objects.

At the end I needed to write all the Objects lost (+- 20).

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2022-06-10 08:43 PM

In response to AlbertoArdila
0 Likes
0
3864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-10 08:43 PM

Hopefully you still have the RemoteConnect project from when it had issues.

You should sent this to your local Schneider Tech Support.  They should investigate and ideally fix the issue within the RemoteConnect environment that caused the problem.

 

If Schneider don't know about, and have an example bad file to work with, then they can't fix the issue, and it's likely to happen again for others (or you when you've forgotten how you fixed it this time).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

ThisIsANightmare
Crewman ThisIsANightmare
Crewman

Posted: ‎2024-09-02 11:59 AM

In response to BevanWeiss
0 Likes
1
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-02 11:59 AM

where can i find advanced options?

Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2024-09-13 02:22 PM

In response to ThisIsANightmare
1 Like
0
2279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-13 02:22 PM

The Advanced Options Bevan is referring to is actually called Advanced Configuration. When you select SCADAPack x70 Logic in the Configuration tree, the Advanced Configuration area is below the Update & Build Logic button. Click the arrow to expand this section, then you'll see the Replace Variables button below, used when a logic variable object available in RemoteConnect is missing in Logic Editor. 

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore