How to sync objects between RemoteConnect and Ecostruxure

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • How to sync objects between RemoteConnect and Ecostruxure
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
75
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All
Related Products
product field
Schneider Electric
RemoteConnect for the SCADAPack x70

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Solved
RussEssex
Crewman RussEssex
Crewman

Posted: ‎2023-11-03 11:44 AM

0 Likes
3
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-03 11:44 AM

How to sync objects between RemoteConnect and Ecostruxure

I am having a pain of a time with this.

RemoteConnect 3.0.3 and EcoStruxure 15.3 (logic editor) for a Scadapack.

I have RemoteConnect and the Logic Editor open.

I create an object in RemoteConnect, how do I get it to appear in the logic editor? 

Or the other way, if I create an object in logic editor, how do I get it to appear in RemoteConnect?

Sometimes the Replace Variables button is enabled in RemoteConnect and I use that, but most of the time that button (and every other button in the Scadapack x70 Logic section is disabled (except the Close Editor button).

 

I have to keep closing and reopening my project to get the Replace Variables button to be enabled, which is a real pain and time waster. 

What is the right way to do this?

Labels
  • Labels:
  • Logic
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2023-11-16 12:20 PM . Last Modified: ‎2023-11-16 12:22 PM

0 Likes
0
1097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-16 12:20 PM . Last Modified: ‎2023-11-16 12:22 PM

If you create a new object in RemoteConnect's Object database, be sure to assign it with a Logic Variable Type of one of the T_SPx70 types. That will ensure that it's shared with Logic Editor.

 

Typically if you're creating a variable in Logic Editor it'll be an Elementary type, with no need to sync with RemoteConnect. But if for some reason you do want to create Derived variables in Logic Editor and then share them with RemoteConnect, here's how to do it:

 

1) First, ensure the project has been Saved in RemoteConnect. This is critical.

2) Now, in Logic Editor you can create the required variables, and assign them a T_SPx70 type. If you're not sure what type to choose, click the [...] "ellipsis" button in the Type column, then look in the Application folder. For example, the type could be T_SPx70_REAL, or T_SPx70_BOOL etc...

3) Back in RemoteConnect, on the SCADAPack x70 Logic page of the Configuration tab, click the "Update & Build Logic" button.

4) Now, in the appropriate area of the Object Configuration page, you'll see the new object.

 

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2023-11-16 12:20 PM . Last Modified: ‎2023-11-16 12:22 PM

0 Likes
0
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-16 12:20 PM . Last Modified: ‎2023-11-16 12:22 PM

If you create a new object in RemoteConnect's Object database, be sure to assign it with a Logic Variable Type of one of the T_SPx70 types. That will ensure that it's shared with Logic Editor.

 

Typically if you're creating a variable in Logic Editor it'll be an Elementary type, with no need to sync with RemoteConnect. But if for some reason you do want to create Derived variables in Logic Editor and then share them with RemoteConnect, here's how to do it:

 

1) First, ensure the project has been Saved in RemoteConnect. This is critical.

2) Now, in Logic Editor you can create the required variables, and assign them a T_SPx70 type. If you're not sure what type to choose, click the [...] "ellipsis" button in the Type column, then look in the Application folder. For example, the type could be T_SPx70_REAL, or T_SPx70_BOOL etc...

3) Back in RemoteConnect, on the SCADAPack x70 Logic page of the Configuration tab, click the "Update & Build Logic" button.

4) Now, in the appropriate area of the Object Configuration page, you'll see the new object.

 

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

ThisIsANightmare
Crewman ThisIsANightmare
Crewman

Posted: ‎2024-08-31 09:17 PM

0 Likes
1
582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-31 09:17 PM

I've followed the proposed solution to a T. Object configuration not updating. this is true with both adding and deleting (using unlock variable). please help

Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2024-09-03 07:31 AM

In response to ThisIsANightmare
0 Likes
0
555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-03 07:31 AM

I'm sorry to hear you're having such troubles with this. Rather than go back and forth slowly here on the forum, I suggest you contact our Global Support Team. They will need to see a copy of your exported project, and will want to know the RTU type and firmware version in the RTU.

 

1-888-226-6876

SupportRO@se.com

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of