Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-14 06:45 AM
When opening a PRJ file I am met with a prompt informing the file has been migrated from an earlier version of Remote Connect. It has blurred the Open Editor button and not allowed me to see the logic.
Is there a way to view files made on older versions in a newer version of RemoteConnect? If not, where can I find older versions of RemoteConnect for download.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-20 09:44 AM . Last Modified: 2025-05-20 09:57 AM
This can be a big issue, and shows why it's important to archive all your projects before upgrading RemoteConnect. The installer does caution users to do this. However, we're past that point now. There are two possible ways to move forward:
1) If you know the version of RemoteConnect the project was created with, you could:
2) Alternately, this method does not require installing the older version:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-16 12:52 AM
I have moved this post to the appropriate forum.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-20 09:44 AM . Last Modified: 2025-05-20 09:57 AM
This can be a big issue, and shows why it's important to archive all your projects before upgrading RemoteConnect. The installer does caution users to do this. However, we're past that point now. There are two possible ways to move forward:
1) If you know the version of RemoteConnect the project was created with, you could:
2) Alternately, this method does not require installing the older version:
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.